Old February 18th, 2021, 09:31 AM   #1
PreLC
Member
United States

PreLC is offline
 
PreLC's Avatar
 
Join Date: Apr 2019
Location: Mars
Posts: 337
Music How do you transmit power and data to removable fixtures?

Hello,

As the name suggests, how do you run power, ethernet and pneumatics to tools/fixtures which are swappable based on part type?

I found some Balluff products: https://www.balluff.com/local/us/pro...tive-couplers/

Turck had some similar ones. They even carry IOLink signals.

But I was wondering how other integrators really do it. Do you have breakouts going to Amphenol connectors, and pneumatics to quick disconnects?

It would need to be IP65 should be adequate, but higher should be okay too.

Regards,
-PreLC
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.
  Reply With Quote
Old February 18th, 2021, 10:00 AM   #2
drforsythe
Member
United States

drforsythe is offline
 
Join Date: Aug 2016
Location: Metro Detroit, Michigan
Posts: 145
I have used the inductive couplers from Balluff and they worked great. The ones I used were for digital I/O only, though.
I use connectors from Ilme (less expensive version of Harting connector, similar to ones provided by Weiland and Contact) for heavier duty and higher density connections. They make an RJ45 version but have not used it yet. There are pneumatic inserts that allow quick connection / disconnection of lower-flow pneumatics like for end effectors.
  Reply With Quote
Old February 18th, 2021, 10:26 AM   #3
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 3,060
for the power we used an electrical plug in coupler with 50 pins. power side was female.
for pneumatics, we used color coded air lines with couplings. for example, blue would be the plant power, the clear would be the return. we used spiral wrap and tied them together as a pair. we did the same for yellow, green, red, orange, gray...... the clear was always the return and we spiral wrapped them together as a pair.
we did not use ethernet, but i would have an ethernet jack on the free end and plug it into a wall outlet jack on the fixture.

i do see two issues with three ethernet.
1. all fixtures will have to have the same address.
2. if these fixtures will be used elsewhere in the plant, they will have to be programmed for the same ip address.
3. these fixtures will have an ip address conflict if everything is connected to a network. you will have to isolate them.
james

Last edited by James Mcquade; February 18th, 2021 at 10:29 AM.
  Reply With Quote
Old February 18th, 2021, 10:47 AM   #4
Drew Ethridge
Lifetime Supporting Member
United States

Drew Ethridge is offline
 
Join Date: Jun 2020
Location: McKinney, TX
Posts: 22
Phoenix Contact make a configurable connector that takes care of power, signals, and Ethernet. Installed thousands of them on a line that was broken down daily by folks that really didn't care how they treated the equipment and they worked fine.

https://www.phoenixcontact.com/onlin...ectors_P-20-08
  Reply With Quote
Old February 18th, 2021, 11:26 AM   #5
PreLC
Member
United States

PreLC is offline
 
PreLC's Avatar
 
Join Date: Apr 2019
Location: Mars
Posts: 337
Quote:
Originally Posted by James Mcquade View Post
for the power we used an electrical plug in coupler with 50 pins. power side was female.
for pneumatics, we used color coded air lines with couplings. for example, blue would be the plant power, the clear would be the return. we used spiral wrap and tied them together as a pair. we did the same for yellow, green, red, orange, gray...... the clear was always the return and we spiral wrapped them together as a pair.
we did not use ethernet, but i would have an ethernet jack on the free end and plug it into a wall outlet jack on the fixture.
Thank you James, very useful. Stupid question, when is a return needed? Also, I like color coding and spiral wrap.
Quote:
Originally Posted by James Mcquade View Post
i do see two issues with three ethernet.
1. all fixtures will have to have the same address.
2. if these fixtures will be used elsewhere in the plant, they will have to be programmed for the same IP address.
3. these fixtures will have an IP address conflict if everything is connected to a network. you will have to isolate them.
Can we not assign them unique IP addresses? Then look at the module's connection state(GOOD/FAULTED) to determine connection? Then drive COP statements for IO based on this connection GOOD?

EDIT: They will be isolated networkwise.
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.

Last edited by PreLC; February 18th, 2021 at 11:33 AM.
  Reply With Quote
Old February 18th, 2021, 11:27 AM   #6
PreLC
Member
United States

PreLC is offline
 
PreLC's Avatar
 
Join Date: Apr 2019
Location: Mars
Posts: 337
Quote:
Originally Posted by Drew Ethridge View Post
Phoenix Contact make a configurable connector that takes care of power, signals, and Ethernet. Installed thousands of them on a line that was broken down daily by folks that really didn't care how they treated the equipment and they worked fine.

https://www.phoenixcontact.com/onlin...ectors_P-20-08
This is great! I'll dig in and see how to configure an RJ45 male/female pair with power!
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.
  Reply With Quote
Old February 18th, 2021, 11:29 AM   #7
PreLC
Member
United States

PreLC is offline
 
PreLC's Avatar
 
Join Date: Apr 2019
Location: Mars
Posts: 337
Quote:
Originally Posted by drforsythe View Post
I have used the inductive couplers from Balluff and they worked great. The ones I used were for digital I/O only, though.
I use connectors from Ilme (less expensive version of Harting connector, similar to ones provided by Weiland and Contact) for heavier duty and higher density connections. They make an RJ45 version but have not used it yet. There are pneumatic inserts that allow quick connection / disconnection of lower-flow pneumatics like for end effectors.
Thanks Doc! I'll look into this more and try to get some in house.
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.
  Reply With Quote
Old February 18th, 2021, 12:13 PM   #8
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 3,060
PreLC,

i do not know your application or your background, but i will try to explain what i am talking about.
when you set up a plc network, you assign the ethernet ip addresses for the plc to look for. for example the plc is 192.168.10.1 and the fixture currently being used is 192.168.10.5. the fixture device is brand x and requires 25 registers for the data.
you now want to use a new fixture that is 192.168.10.25 and is brand y.
the plc is looking for the 10.5 address, not the 10.25 address. you now have 2 options. either go online with the plc and change the address of the fixture to look for (10.25), or take the fixture somewhere, power it up, and change its address to 10.5. either way, this is downtime every time you change the fixture. try doing this every hour, 24 hours a day and on multiple machines
if i am incorrect, someone please correct me.
james
  Reply With Quote
Old February 18th, 2021, 12:45 PM   #9
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 478
Quote:
Originally Posted by James Mcquade View Post
PreLC,

i do not know your application or your background, but i will try to explain what i am talking about.
when you set up a plc network, you assign the ethernet ip addresses for the plc to look for. for example the plc is 192.168.10.1 and the fixture currently being used is 192.168.10.5. the fixture device is brand x and requires 25 registers for the data.
you now want to use a new fixture that is 192.168.10.25 and is brand y.
the plc is looking for the 10.5 address, not the 10.25 address. you now have 2 options. either go online with the plc and change the address of the fixture to look for (10.25), or take the fixture somewhere, power it up, and change its address to 10.5. either way, this is downtime every time you change the fixture. try doing this every hour, 24 hours a day and on multiple machines
if i am incorrect, someone please correct me.
james
James,

In Rockwell land you can inhibit modules using the SSV instruction. You can add all the fixtures in your IO tree and then inhibit all that are not being used.

Obviously you will need some sort of config screen or selector switch to implement this but it is possible for the fixtures to have unique IP addresses.
  Reply With Quote
Old February 18th, 2021, 01:04 PM   #10
atc222
Member
United States

atc222 is offline
 
Join Date: Jun 2019
Location: New York
Posts: 35
Clever Dock,

You could also leave all in tree and and use communications status to determine which fixture currently connected...
  Reply With Quote
Old February 18th, 2021, 01:08 PM   #11
PreLC
Member
United States

PreLC is offline
 
PreLC's Avatar
 
Join Date: Apr 2019
Location: Mars
Posts: 337
Quote:
Originally Posted by _Dock_ View Post
James,

In Rockwell land you can inhibit modules using the SSV instruction. You can add all the fixtures in your IO tree and then inhibit all that are not being used.

Obviously you will need some sort of config screen or selector switch to implement this but it is possible for the fixtures to have unique IP addresses.
Hi Dock, also, can't we just let them error out? If they aren't connected, and physical conditions indicate this, isn't inhibition/uninhibition unnecessary?
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.
  Reply With Quote
Old February 18th, 2021, 01:17 PM   #12
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,867
Quote:
Originally Posted by Drew Ethridge View Post
Phoenix Contact make a configurable connector that takes care of power, signals, and Ethernet. Installed thousands of them on a line that was broken down daily by folks that really didn't care how they treated the equipment and they worked fine.

https://www.phoenixcontact.com/onlin...ectors_P-20-08
I use these also. I also jump out one set of pins on the male side of the connector to use as verification that the unit is plugged in.
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old February 18th, 2021, 01:18 PM   #13
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 3,084
One thing we used to do is for 415v to disable it & check connectors are plugged in is have a return loop so that the main panel knows all plugs have been plugged in and enables the 415v power cables, I also like the colour coded air lines.
  Reply With Quote
Old February 18th, 2021, 01:33 PM   #14
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 478
Quote:
Originally Posted by PreLC View Post
Hi Dock, also, can't we just let them error out? If they aren't connected, and physical conditions indicate this, isn't inhibition/uninhibition unnecessary?
You certainly could. However I do not, mainly because your IO status light will be flashing (send maintenance on a fritz) and I monitor the IO status in alarms to signal if it occurs.

The main reason why I do this is because of how powerflex drives ethernet loss bit functions. I know that this doesn't apply to all but this specific situation is why I use the SSV.


On power up if a powerflex drive does not establish a connection the ENet loss bit will not be true. The only way to detect this is from the IO status in GSV.

If a powerflex establishes a connection THEN loses it the Enet loss bit will be true, which you can monitor. The only way I know to detect a no connection on a drive on power up is to use the IO status GSV.
  Reply With Quote
Old February 18th, 2021, 01:37 PM   #15
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 478
Quote:
Originally Posted by atc222 View Post
Clever Dock,

You could also leave all in tree and and use communications status to determine which fixture currently connected...

Correct, this would be another layer to be able to recognize operator errors.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Retentive data lost Micrologix1000 Deer LIVE PLC Questions And Answers 22 February 1st, 2021 12:16 PM
Suggestions for data logging power quality analyzer? defcon.klaxon LIVE PLC Questions And Answers 12 September 19th, 2018 07:42 AM
How to get data from AB power monitor 1420-V1-ENT minaykha LIVE PLC Questions And Answers 3 August 25th, 2015 03:33 AM
Power Outage Data Memory Issue DKahmer LIVE PLC Questions And Answers 2 October 5th, 2011 02:28 PM
SLC 5/03 can not keep data when AC power off Tony2006 LIVE PLC Questions And Answers 3 December 16th, 2006 10:26 AM


All times are GMT -4. The time now is 11:19 AM.


.