Old December 2nd, 2007, 04:18 PM   #1
Arlie
Member
United States

Arlie is offline
 
Arlie's Avatar
 
Join Date: Jun 2007
Location: Ellenville,NY
Posts: 83
Red face PID control

can someone help me out with pid control with ramp??

i understand the principle but not how it actually works or how to program it.

I am using FPWINPRO to prog a Panasonic FPX plc
  Reply With Quote
Old December 2nd, 2007, 07:19 PM   #2
Lancie1
Lifetime Supporting Member
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 9,999
Arlie,

I have set up ramp functions using a timer. You set up a RAMP mode of control, which takes over the PID SETPOINT temporarily. You decide how long it should be between start and full setpoint of the PID. Then you simply move a low beginning number into your SETPOINT location. A good method is to set the beginning setpoint equal to the current process variable.

The time interval between setpoint changes depends on the process and how fast you want to ramp it. Suppose you have a furnace that needs to be heated to 1800 degrees over a 1-hour period (to avoid stressing the refractory material). Your program calculates this: 3600 seconds/(1800-Present Temperature) = Time interval for each 1-degree setpoint change. If the current furnace temperature is 100 degrees, this comes out to 2.11 seconds per degree. You may want to truncate the fraction and set your timer for 2 seconds, a more practical number.

Then say you set the beginning setpoint to 100, and every 2 seconds, you ADD 1 to the SETPOINT, until the final desired setpoint 1800 is reached. When the setpoint = 1800, you disable the RAMP mode.

If your controls are working correctly, and you have allowed enough response time, your process variable should move along with the setpoint as it ramps up.

Last edited by Lancie1; December 2nd, 2007 at 07:39 PM.
  Reply With Quote
Old December 3rd, 2007, 08:22 AM   #3
Arlie
Member
United States

Arlie is offline
 
Arlie's Avatar
 
Join Date: Jun 2007
Location: Ellenville,NY
Posts: 83
Ok so assuming that all goes well with the ramp , once setpoint is reached PID control will take over and run the process??

what about overshoot? how do you prevent or at least limit that??
  Reply With Quote
Old December 3rd, 2007, 09:30 AM   #4
Krcedinac
Member
Serbia

Krcedinac is offline
 
Krcedinac's Avatar
 
Join Date: Jul 2006
Location: Krca
Posts: 163
You have to adjust PID parameters...use search engine, ther is a lot of good topics on that subject on this forum
  Reply With Quote
Old December 3rd, 2007, 09:59 AM   #5
Lancie1
Lifetime Supporting Member
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 9,999
Ok so assuming that all goes well with the ramp , once setpoint is reached PID control will take over and run the process??
ANSWER: Yes. Actually the PID is always controlling the process variable (during the ramp-up also). All the "ramp" does is automatically increment the setpoint during some pre-defined time period. It is the PID's job to make sure the Process Variable follows the Setpoint.

What about overshoot? How do you prevent or at least limit that??
ANSWER: Adjust your PID tuning parameters until overshoot is minimized. I am no expert in how to make that adjustment, but search the posts here by Ron Beaufort for methods to do that.

Now, if the long ramp up from a low starting point is what causes the overshoot (because the PID is tuned for the best control around the normal operating point), then lower your ending ramp setpoint so the overshoot (only caused by the ramp-up) is reduced or at least tolerable. You can add a second ramp timer to bump the setpoint on up, after the process has stabilized, or let the operator bump it up manually when he sees the process variable level out.

Last edited by Lancie1; December 3rd, 2007 at 10:33 AM.
  Reply With Quote
Old December 3rd, 2007, 11:15 AM   #6
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: United Welfare States of America
Posts: 7,395
What is the purpose of having a ramp?

If it is to keep the temperature rate from becoming too high then OK but if you just need to avoid over shoot then you should only need to tune the PID so the response is critically damped or over damped.

The first thing to do is get response data. This is the control output and PV as a function of time. There should be some transients so the plant time constants and dead time can be determined accurately. See www.controlguru.com for the basics.
  Reply With Quote
Old December 3rd, 2007, 03:21 PM   #7
tiopaeng
Member
United States

tiopaeng is offline
 
Join Date: Sep 2007
Location: CA
Posts: 20
I have the same project of ramping the temperature but I don't know how to output to an SCR controller with 4-20mA input. If anybody can share info and examples I'd greatly appreciate it.

Thank you,
TioPaeng
  Reply With Quote
Old December 3rd, 2007, 03:31 PM   #8
CroCop
Member
United States

CroCop is offline
 
Join Date: Aug 2005
Location: Utah
Posts: 1,050
Quote:
Originally Posted by Peter Nachtwey
What is the purpose of having a ramp?
To avoid thermal shock in a heating type system (I'm sure there are many other reasons as well, but I do ALOT of heat controls). Some systems do not enjoy sudden changes in their process value. Some folks use a built in ramp, others roll their own.
  Reply With Quote
Old December 3rd, 2007, 03:53 PM   #9
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 4,178
CroCop-


I think that is what Peter was referring to here:

Quote:
Originally posted by Peter Nachtwey:
If it is to keep the temperature rate from becoming too high then OK ...

Peter is correct about tuning assuming that the PI implementation correctly handles integral limits. If the PI implementation simply limits the integral sum to the maximum output and doesn't modify this by the proportional contribution, then you will still get overshoot to a large signal step command no matter how carefully it is tuned. In a system such as this you can at least give yourself a chance of limiting overshoot by ramping the command at a rate that keeps the system out of saturation.

Keith
  Reply With Quote
Old December 4th, 2007, 04:14 AM   #10
Andybr
Member
United Kingdom

Andybr is offline
 
Join Date: Oct 2004
Posts: 588
If the purpose of the ramp is to gradually bring the system up to temperature as is normal for steam heating then I normally ramp the CV upper limit rather than the SP. This prevents the possibility of overshoot early in the ramp and allows you to tune the system for optimum performance at the normal setpoint rather than for setpoint changes.

Andybr
  Reply With Quote
Old December 4th, 2007, 10:26 PM   #11
Lancie1
Lifetime Supporting Member
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 9,999
Quote:
If the purpose of the ramp is to gradually bring the system up to temperature as is normal for steam heating then I normally ramp the CV upper limit rather than the SP.
I suppose that for a steam heating system you want to gradually open the steam valve to avoid putting a large amount of heat into cold pipes. That is a totaly different situation than the furnace that I mentioned earlier. There was no problem with opening the CV to 100% as soon as the burner was lighted.

The manufacturer's warranty for the furnace specifically said that if the temperature inside the furnace climbed to 1800 degrees in less than 1 hour, then the warranty was null and void and the manufacturer would assume no liability for repair of the unit. They were terribly concerned about the process temperature rate-of-rise. They did not really care that the CV (Control Variable) had made it to the 100% maximum upper limit several times during that 1 hour. It always did. The firing rate gas valve would stay 100% open for the first 20 to 25 minutes.

I do not think that PID control alone could insure this rate-of-temperature-rise limitation, nor could ramping of the Control Variable. Ramping of the CV would have made the heat-up period drag out for 7 or 8 hours, instead of 1 hour.

At 200 degrees, the overshoot was 100 degrees or more, but who cared? At about 350 degrees, the Setpoint ramp caught up with the furnace temperature overshoot, and from there up to 1800 it was a nice smooth-line lock-step climb. with the temperature closely following the setpoint. The operating point was always 1800, and that was where the control had to be very sensitive. I tuned the PID loop so that as it neared 1800 degrees, the overshoot dropped to 1 degree and undershoot was 1 degree. We did not care about anywhere else, as long as it kept heating gradually over that 1-hour period.

The Setpoint ramp did the job.

Last edited by Lancie1; December 4th, 2007 at 11:17 PM.
  Reply With Quote
Old December 5th, 2007, 04:08 AM   #12
burnerman
Member
England

burnerman is offline
 
Join Date: Nov 2005
Location: Huddersfield
Posts: 212
Quote:
Originally Posted by Lancie1
I do not think that PID control alone could insure this rate-of-temperature-rise limitation, nor could ramping of the Control Variable. Ramping of the CV would have made the heat-up period drag out for 7 or 8 hours, instead of 1 hour.
Many furnaces and high temperature applications require the temperature rate of rise to be limited to avoid thermal shock to the refractories which can easily be damaged if the thermal gradient between the hot and cold face is too high.

I've worked on countless applications like this and PID control - correctly tuned - with setpoint ramping can easily manage the required rate of rise to the degree (providing the controlling equipment, e.g. burners, valves, etc. is up to the job). Ramping the setpoint can only help minimise overshoot compared to bringing the temperature up from cold to a fixed setpoint.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
???Control Logixs 5000 PID Temp Control???? pater01 LIVE PLC Questions And Answers 26 July 24th, 2006 08:09 PM
[S7] PID control between control valve and load cell ascoldasice LIVE PLC Questions And Answers 4 July 20th, 2006 11:42 AM
PID for Web Tension Control scottmurphy LIVE PLC Questions And Answers 19 May 18th, 2005 05:47 PM
AB PLC5 PIDs Derek McFarland LIVE PLC Questions And Answers 23 March 2nd, 2005 02:18 AM
PID - MicroLogix Temperature Control Peter Nachtwey LIVE PLC Questions And Answers 112 October 11th, 2004 12:18 PM