plc 120v relay outputs to device with 24v npn input

tclark

Member
Join Date
Mar 2021
Location
Texas
Posts
1
I'm not sure the best way to do this. I've got an old GE plc with only 120V relay outputs. I'm replacing a UV light component with an LED controller that has 24VDC NPN inputs. It seems like I could use a relay with 120VAC coil to switch 24VDC, but what kind of relay is that -SPST? And how to best "flip" the signal for NPN? Go into the program and make the existing coil into a nc contact?

Thanks in advance for any ideas!
 
Do you only need to change the voltage on a single output or on more than one? Your terminology raises a question.
There are 120 VAC PLC outputs and there a relay contact PLC outputs. Relay contact outputs can switch 24 VDC as well as 120 VAC. You just need to rewire the circuit. Some relay contact output modules feature isolated output points, while others feature a group of output points sharing a common. Best to identify the part number of the module you're dealing with.
 
I'm not sure the best way to do this. I've got an old GE plc with only 120V relay outputs. I'm replacing a UV light component with an LED controller that has 24VDC NPN inputs. It seems like I could use a relay with 120VAC coil to switch 24VDC, but what kind of relay is that -SPST? And how to best "flip" the signal for NPN? Go into the program and make the existing coil into a nc contact?

Thanks in advance for any ideas!

You can get a SPDT interposing relay that mounts on a DIN rail.

https://www.automationdirect.com/ad...ectro-mechanical_relays/slim_interface_relays

I used one made by AB today. Same thing, pretty much. Just a bit more expensive.
 

Similar Topics

I know this topic has been brought up a few times, but i had some specific questions. I have installed several 1783-NATR devices and they have...
Replies
0
Views
10
Hello We have installed several G.E. Fanuc 90 70 PLC Everything was ok but suddenly we can not communicate anymore with any PLC with the software...
Replies
0
Views
26
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
46
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
84
How to fix if appears code “$115 plc-restart running” on the screen OP17
Replies
3
Views
123
Back
Top Bottom