Unable to communicate between HMI & PLC KINCO

wiwie

Member
Join Date
Jun 2008
Location
PASURUAN
Posts
17
Can anyone help me getting this communications connection set up between KINCO GL100 and KINCO K508-40AR?


I am using Port 1(RS485) on the KINCO PLC, set in Mosbus Master with port settings
Baud Rate 9600
Stop Bits 1
Parity None
Data Bits 8
Address 1


In the KINCO HMI I am using Com0,RS485
Communication protocol Kinco PLC Series

Baud Rate 9600
Stop Bits 1
Parity None
Data Bits 8
Station 1


I have made a cable up to run from the HMI to PLC as follows

HMI 9 Pin D plug PLC 9 Pin D plug
1 RX- -------------------------------- 3B
6 RX+ -------------------------------- 2A


Using this configuration appear PLC no response on the HMI

Any help would be appreciated
 
In the manual they do not show pin 5 ground. I'm pretty sure you need it too.I think both HMI and PLC use pin 5 for ground.


RS485-2 need three wire A, B data and ground.
 

Similar Topics

Hi, i have fx5u plc. Want to communicate with citect scada. Have tried multiple protocol but it's not communicated. Can any one help in this topic.
Replies
4
Views
1,809
Can anyone help me getting this comms connection set up? I am using Port 2 on the Versamax ICU200UDR005-DK, set in SNP with port settings Baud...
Replies
4
Views
1,540
Hey, I have factorytalk studio ME version9.it will generate "unable to communicate with the factory talk linx server localhost" every time I try...
Replies
3
Views
3,680
Hello everyone, I am stuck here with an OP77A HMI, the problem I am facing is that I am unable to open its loader as its startup delay(as I think)...
Replies
11
Views
3,300
We have an HMI that when an application is loaded the HMI it asks if you want to change the terminal configuration settings to match the...
Replies
4
Views
3,147
Back
Top Bottom