how can i connect one load cell with two load cell modules?
HamzaAhmed
Aug 2020
Palestine
86
Hello guys,
I have a load cell connected with Siemens load cell module, i want to add Delta load cell module and take a signal only from the load cell without give it an excitation from Delta load cell module.
I tried the previous way but it didn't work the weight is not stable, so i am thinking to connect the load cell modules the delta and siemens with the same power supply and connect all wires without cut the excitation. could that works?
Do any one have an instead solation?
Thanks,
I am not 100% sure, my first reaction would be it cannot be done. I think it is either highly unusual to do as you intend to do, or it just plain does not work.
What might perhaps work, is if one of the amplifiers (or digitizers) is 6-wire. You would then not use the excitation voltage from this device, but you would connect the sense wires. Not sure if this actually works though. I'm sure there are folks more knowledgable than me who can elaborate.
Why would you want to do this, can you explain the reason behind your question?
Typically with multiple load cells toy need a summing board to combine the signals for all the load cells and give 1 signal of the combined cells
Any of the scale manufactures should be able to supply you with what you need
That is the reverse of what HamzaAhmed asked for, Gary. He doesn't need to wire multiple load cells to one input. Rather he asked for a way to use one single load cell with more than one amplifier (or digitizer). That is not resolved by use of a summing board.
Thanks for your answer, the reason is mu customer bought a manufature with full automation, but i did a better system and automation but he want to monitor and see the scales with the two systems.
yes you are right
Your only actual solution, would be to use a Dual Bridge Load Cell.
Several companies make them.
A single bridge won't work, as each amplifier is going to want to supply its own excitation. Yes, it is technically possible to excite a strain gauge from one amplifier, and read it on another, but then you aren't actually evaluating the actual operation of the system.
Is there a network between the Siemens and the Delta? Perhaps only one of them could make the actual measurement i.e. connect to the load cell, and the other could get the value from there e.g. Modbus or similar?
Seems great.
I didn't hear about dual bridge load cell before.
Thanks a lot
Yes you are right, but i didn't know the Siemens plc code and it's not supporting Modbus as i know , and i don't want to edit it because of grantee issues.
Do have a way to see all modbus registers and values at the same time?
Hey guys. It's been quite some time since I've messed with FTV SE. I just got the software and activation for SE V. 11.00. I've tried to upload an...
2,021
My memory is failing me. I seems to remember I could download which ever version of any Rockwell Automation software as long as they are covered...
2,510
I have a micro820 in the field that I downloaded to yesterday. It said it was downloading the ethernet settings (even though they did not change)...
2,743
START FROM ZERO. I had a sharpening machine using S7-200 CN. I don't have PG or software or communication cables. What is the software/cable to...
2,396
87