Gx Works 2 Timers Problem
bozkiraz
Jun 2021
Ankara
Hello all. I have a problem about timers. I have fx3u-24mr. The program is running in simulation mode . But in monitoring mode M77 won't power up when I try to implement on it. Can you help me?
You are using the same instance of the IEC timer i.e. Timer_1
Rename the second timer as Timer_2.
Using the same instance one will override the other.
So double click on the second timer will bring up the label registration and type in a new instance name, accept it. Note: if you need to use any variables in other than that program block they must be declared as global variables
Local variables only work within that program block.
Also you do not need the coil on the output if it's being used within the same block you can use the Timer_1.Q as a contact but if it makes your code more readable then use a coil.
Actually they are the same timers. The first is in simulation mode and the second is in monitoring mode. I've attached pictures to show what the problem is.
Ah I see, it looked like two rungs in the same program.
So you say that if you run in simulation it works but in the real PLC it does not.
Just for information is this a genuine FX3U or one of those clones.
Just try using a different "M" number first to see if that cures the problem I know there can be some issues with clones.
What is your time setting it must be in timer type i.e. milliseconds I notice you are using a tag rather than using a fixed timer value, even though these timers are based on 100ms per count the value must be in ms. so your timer value must be 500, it is known that sometimes a timer will not trigger if the time setting is set to 0.
Also noticed that the timer preset variable is not displaying the value ? this is not right have you set the variable as a "TIME" variable
Hey everyone and anyone that can lend a helping hand. I have a project that I am being asked to add some animations of Solidworks or "3D" models...
333
PLC: Fx5u CPU As Per manual High Speed Input Module can add from Navigation window  [Parameter]  [Module Information]  Right-click  [Add New...
98
Hi all, anyone does have experience in Gx Works 2? Currently I having an issue which is when certain device added from MELSOFT Navigator and...
110
Hi Guys, I want to connect my 1769-L36ERM to a different network domain, is it possible to do it using only the dual ports in the Controller? Or...
221
I'm totally new to PLC's and I've just purchased an FX3U-14MR Mitsubishi Clone. I believe I need to use GX Works Software to program it but I've...
125