Possibly wrong firmware? PV600

I recently went to install a new PV at one of our machines. Backstory
Old PV Part number
2711-T6C16L1 SER (B) REV (C) FRN (4.43)


New PV Part Number
2711-T6C5L1 SER (A) REV (D) FRN (4.2)


Now I could not connect to the new PV so I brought the old PV back up to the machine to reconnect to it to verify my computer and cables were acting accordingly.

OldPV
I open RSLINX and went to new RS232 DF1 devices and clicked on Auto configure and BAM it connected with no issues.



When I disconnect the cable from the OLD PV and plug it into the NEWPV the new one never shows up.

So I stop the driver and delete it, I am still plugged into the NewPV and went to new Rs232 df1 devices and clicked on AUto configure. In the space besides that it comes up can not configure check your switches and cables.

Since the models have different SER REV and FRN is there a Possibilty of a firmware difference that will not allow me to even see the new PV in RSLINX.

Could it be that RSLINX is out of date (I am not sure if it is.) And or the PV 's firmware is out of date and they are compatible.
I kinda in uncharted territory and at least the Engineer at my plant was kinda stumped.
My next step is call AB personally to see what the issue can be.

THanks for reading all this.
  Reply With Quote
Old November 15th, 2018, 06:18 PM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,983
There's an uh-oh in your part numbers.
Old PV Part number
2711-T6C16L1
RS-232 (DF1)

New PV Part Number
2711-T6C5L1
RS-232 (DH-485)

So to use the DH485 model, you will need to modify the PB32 file to match the hardware, and use your 1747-UIC adapter to dump it in. Additionally, the device that connects to that port will need to be capable of supporting the DH485 protocol and it will need to be configured correctly too.

The firmware difference is less of a concern than the Series letter, but since we're comparing granny smiths to red delicious, that probably doesn't matter either.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

Last edited by OkiePC; November 15th, 2018 at 06:24 PM.
  Reply With Quote
Old November 15th, 2018, 06:26 PM   #3
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 33
Quote:
Originally Posted by OkiePC View Post
There's an uh-oh in your part numbers.
Old PV Part number
2711-T6C16L1
RS-232 (DF1)

New PV Part Number
2711-T6C5L1
RS-232 (DH-485)

So to use the DH485 model, you will need to modify the PB32 file to match the hardware, and use your 1747-UIC adapter to dump it in.

The firmware difference is less of a concern than the Series letter, but since we're comparing granny smiths to red delicious, that probably doesn't matter either.
Yes, I know they are different but it is what my company guy sent us lol.

I used com port 1 via AB serial cable to the RS232 PORT behind the 24VDC to connect to the OLD PV. Not the DF1 port Just clarifying since you did post in my last thread.

The PB32 file is not the issue I am having. I can't connect to the PV at all
  Reply With Quote
Old November 15th, 2018, 06:31 PM   #4
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,983
They are both RS232 (apples) but one is DF1, the other is DH485 (protocol flavors). So the problem is with the language they speak, which will be a problem with the file and the way you connect to it as well as how you set up the RSLinx driver. The port you use to download will (I assume) be the same port it will use to "talk" to the PLC when you get done...

So that PLC needs to be bilingual too. Problem is, the PLC will need to be told what protocol to use, and with DH485 will need to be assigned a compatible node number. If your company policy allows, share with us a copy of the latest and greatest PLC file and the PB32 file, and we can 1) see if it is possible. 2) help you be the hero and tell the guy who sent you the wrong part you made it work despite him.

EDIT: tell us what version of RSLinx you are running. Mine has a driver for the UIC (version 4.00). I think with some older versions, you had to do something less intuitive to use the UIC adapter. But if you go to RSLinx Configure drivers and look in the available driver types for "DH485 UIC devices" then you should be good to go there...
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

Last edited by OkiePC; November 15th, 2018 at 06:39 PM.
  Reply With Quote
Old November 15th, 2018, 06:50 PM   #5
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 33
Quote:
Originally Posted by OkiePC View Post
The port you use to download will (I assume) be the same port it will use to "talk" to the PLC when you get done...
.
The old PV had the RS232 DF1 port (expansion card/printer port connection) on the right side of the panel that connected to the SLC 5/03. It is it's own separate card. I uploaded the program from this panel via the normal RS232 NOT the df1 side.

The new PV has the spot for this card/port but did not come with it.

I can get the files for both the PV and plc. Be around 7am EST. Not sure if I can upload those here or email them to whom may want to look. I had to use Tinypic for pics since I couldn't get them to upload right on here. I couldnt see them.
  Reply With Quote
Old November 15th, 2018, 06:53 PM   #6
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 33
Quote:
Originally Posted by OkiePC View Post
EDIT: tell us what version of RSLinx you are running. Mine has a driver for the UIC (version 4.00). I think with some older versions, you had to do something less intuitive to use the UIC adapter. But if you go to RSLinx Configure drivers and look in the available driver types for "DH485 UIC devices" then you should be good to go there...
I will look when I get to work in the morning. I am not using the UIC adapter to connect to the PV. I only use it to connect to the PLC.

Thanks OkiePC
  Reply With Quote
Old November 15th, 2018, 06:55 PM   #7
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,983
To attach files, create a compressed folder and put both files in it. Then when making a reply, hit the "Go Advanced" button below the text window and look for the "Attach Files" button, follow directions from there.

Can you tell us the make and model of the PLC? We might be wasting your time depending on what you've got.

Also, I am pretty sure (99.5%) that you cannot install an additional card in the Panelview Standard. I have in the past swapped out touchpanels between very similar models, but this procedure involves some risk. If the old Panelview just has a bad touch cell, that might be worth considering.

It's things like this that have caused me to always opt to upgrade to a Red Lion HMI at first sign of trouble with any Painelview model. Almost any of the Red Lion offerings can replace any Panelview or PV+ that is not using DH+ or RIO (blue hose).
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

Last edited by OkiePC; November 15th, 2018 at 06:58 PM.
  Reply With Quote
Old November 15th, 2018, 07:06 PM   #8
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 33
Quote:
Originally Posted by OkiePC View Post
Can you tell us the make and model of the PLC? We might be wasting your time depending on what you've got.

Also, I am pretty sure (99.5%) that you cannot install an additional card in the Panelview Standard. I have in the past swapped out touchpanels between very similar models, but this procedure involves some risk. If the old Panelview just has a bad touch cell, that might be worth considering.

It's things like this that have caused me to always opt to upgrade to a Red Lion HMI at first sign of trouble with any Painelview model. Almost any of the Red Lion offerings can replace any Panelview or PV+ that is not using DH+ or RIO (blue hose).
THis is the pic of the SLC.
  Reply With Quote
Old November 15th, 2018, 08:51 PM   #9
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,983
The RS232 port (with the DB9 connector plugged in) is connected to the PV, correct?

If so, then we can modify the SLC and the PV programming to accommodate your new hardware. I will have to dig in the manual at work tomorrow to make sure that no changes are required to the cable...pretty sure you can even do this online without having to download. You might have to switch the CPU to program mode briefly (stopping the process it controls).

We'll still need you to share that PB32 file or walk you through the changes needed to pick the right catalog number.

My recommendation for DH485 node numbers:
RSLinx UIC driver Node 0 (default)
PLC port node 1 (defaults)
HMI node 2
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old November 16th, 2018, 08:04 AM   #10
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 33
OkiePC Here is the plc and pb32 file.

I have a SD card with the program from the old PV on it.
When I put the card into the NEWPV and load from CARD, it says file not supported.

This is the type of file that it supports


This is the type of file that is saved on the disc
Attached Files
File Type: zip PV.zip (110.3 KB, 2 views)
  Reply With Quote
Old November 16th, 2018, 08:09 AM   #11
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 33
Quote:
Originally Posted by OkiePC View Post
They are both RS232 (apples) but one is DF1, the other is DH485 (protocol flavors). So the problem is with the language they speak, which will be a problem with the file and the way you connect to it as well as how you set up the RSLinx driver. The port you use to download will (I assume) be the same port it will use to "talk" to the PLC when you get done...

So that PLC needs to be bilingual too. Problem is, the PLC will need to be told what protocol to use, and with DH485 will need to be assigned a compatible node number. If your company policy allows, share with us a copy of the latest and greatest PLC file and the PB32 file, and we can 1) see if it is possible. 2) help you be the hero and tell the guy who sent you the wrong part you made it work despite him.

EDIT: tell us what version of RSLinx you are running. Mine has a driver for the UIC (version 4.00). I think with some older versions, you had to do something less intuitive to use the UIC adapter. But if you go to RSLinx Configure drivers and look in the available driver types for "DH485 UIC devices" then you should be good to go there...
RSLINX Classic Lite Rev 3.90.00 CPR 9 SR 9
i do see the DH485 for UIC devices for in the RSLinx drivers.

Last edited by Leukic; November 16th, 2018 at 08:17 AM.
  Reply With Quote
Old November 16th, 2018, 08:12 AM   #12
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 33
Quote:
Originally Posted by OkiePC View Post
They are both RS232 (apples) but one is DF1, the other is DH485 (protocol flavors). So the problem is with the language they speak, which will be a problem with the file and the way you connect to it as well as how you set up the RSLinx driver. The port you use to download will (I assume) be the same port it will use to "talk" to the PLC when you get done...

So that PLC needs to be bilingual too. Problem is, the PLC will need to be told what protocol to use, and with DH485 will need to be assigned a compatible node number. If your company policy allows, share with us a copy of the latest and greatest PLC file and the PB32 file, and we can 1) see if it is possible. 2) help you be the hero and tell the guy who sent you the wrong part you made it work despite him.

EDIT: tell us what version of RSLinx you are running. Mine has a driver for the UIC (version 4.00). I think with some older versions, you had to do something less intuitive to use the UIC adapter. But if you go to RSLinx Configure drivers and look in the available driver types for "DH485 UIC devices" then you should be good to go there...
Quote:
Originally Posted by OkiePC View Post
The RS232 port (with the DB9 connector plugged in) is connected to the PV, correct?

If so, then we can modify the SLC and the PV programming to accommodate your new hardware. I will have to dig in the manual at work tomorrow to make sure that no changes are required to the cable...pretty sure you can even do this online without having to download. You might have to switch the CPU to program mode briefly (stopping the process it controls).
On the old PV the rs232 DF1 port talked to the plc.
I retrieved the program from the old Pv via the rs232 port that doesnt talk to plc.
  Reply With Quote
Old November 16th, 2018, 08:26 AM   #13
BruceJW
Member
South Africa

BruceJW is offline
 
Join Date: Jan 2006
Location: Randburg
Posts: 55
Hi,

Maybe this is your issue?
Attached Images
File Type: jpg Capture.JPG (128.1 KB, 36 views)
  Reply With Quote
Old November 16th, 2018, 08:50 AM   #14
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 33
BruceJW. When I installed the rs232 df1 card into the new Pv that was the printer port. Because since I removed the card. It says there is not printer port installed. The only port on the new panel is the rs232 port and the slot for the Sd card. Which in previous post I just made wondering why the file is not supported
Thanks for the help. I will see if I come up with something.
  Reply With Quote
Old November 16th, 2018, 08:54 AM   #15
BruceJW
Member
South Africa

BruceJW is offline
 
Join Date: Jan 2006
Location: Randburg
Posts: 55
Quote:
Originally Posted by Leukic View Post
BruceJW. When I installed the rs232 df1 card into the new Pv that was the printer port. Because since I removed the card. It says there is not printer port installed. The only port on the new panel is the rs232 port and the slot for the Sd card. Which in previous post I just made wondering why the file is not supported
Thanks for the help. I will see if I come up with something.
good luck, I have always avoided Panel Views, hence not worked with them much. With DH485, you can apparently bridge to PV via the SLC. Assuming you have a valid DH485 network.

edit, with hours you already spent fault finding, can I suggest you look at upgrading to the latest offerings?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1756-ENBT firmware upgrade epicnote LIVE PLC Questions And Answers 3 February 11th, 2014 08:18 PM
RSLogix 5000 Installation of Firmware Joel201 LIVE PLC Questions And Answers 8 January 26th, 2014 07:02 PM
Compactlogix Firmware OkiePC LIVE PLC Questions And Answers 6 June 26th, 2010 01:16 PM
CLX with PF700VC on ENET firmware problems V16? or V17? AndrewB LIVE PLC Questions And Answers 0 April 20th, 2010 12:03 AM
1756 ENBT Module - Firmware detail jm.shafi LIVE PLC Questions And Answers 5 September 23rd, 2009 02:58 AM


All times are GMT -5. The time now is 09:11 AM.


.