Micrologix 1400 "Fast" inputs

I am looking to see what is defined as fast inputs. Is this just another way of denoting HSC inputs? I am looking at the manual (1766-UM001M-EN-P) and the only reference to the word fast in the entire thing (if the find feature is to be believed) is on page 16 when talking about the inputs themselves.

Thank you in advance.
  Reply With Quote
Old November 16th, 2018, 02:01 PM   #2
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 838
Code:
 Twelve high-speed inputs (except 1766-L32AWA and 1766-L32AWAA controllers) 
that can be used individually as latching (pulse-catch) inputs, event interrupts, or 
alternately combined as three 100 kHz high-speed counters featuring 10 modes of 
operation.
This came from the product selection guide. So the answer to your question is that they *can* be HSC inputs. Here is the selection guide:

https://www.google.com/url?sa=t&source=web&rct=j&url=https://literature.rockwellautomation.com/idc/groups/literature/documents/sg/1761-sg001_-en-p.pdf&ved=2ahUKEwiih_u6ytneAhWq6oMKHZCPBkAQFjAIegQ IBBAB&usg=AOvVaw0wv_ROQC8AMa-h6sgh4kdp&cshid=1542394325918"
  Reply With Quote
Old November 16th, 2018, 02:25 PM   #3
locotumbler
Member
United States

locotumbler is offline
 
Join Date: Jan 2013
Location: Otsego, MN
Posts: 80
Thank you. I am not looking to use them as a HSC but the 1200 I am replacing misses one of my sensor signals from time to time.
  Reply With Quote
Old November 16th, 2018, 02:51 PM   #4
roxusa
Lifetime Supporting Member
United States

roxusa is offline
 
Join Date: Nov 2008
Location: NJ
Posts: 663
Are you replacing the 1200 with a 1400
__________________
B.Pedersen
if you are going to assume, assume your wrong.
  Reply With Quote
Old November 16th, 2018, 03:08 PM   #5
locotumbler
Member
United States

locotumbler is offline
 
Join Date: Jan 2013
Location: Otsego, MN
Posts: 80
Yes. I am replacing a 1200 with a 1400. We are upgrading the programming and adding a PC based hmi so we need the network port.
  Reply With Quote
Old November 16th, 2018, 05:06 PM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,292
Yup; the first 12 inputs can be used with HSC or with interrupts for pulse-catching or discrete input interrupt features. You're on the right track !
  Reply With Quote
Old November 16th, 2018, 06:17 PM   #7
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,983
Quote:
Originally Posted by locotumbler View Post
Thank you. I am not looking to use them as a HSC but the 1200 I am replacing misses one of my sensor signals from time to time.
Check the base input filter settings and compare with the duration of the sensor signal. It might be that you need to adjust the base input filter to detect pulses of a shorter duration.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old November 18th, 2018, 01:01 PM   #8
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,484
Quote:
Originally Posted by locotumbler
I am looking to see what is defined as fast inputs. Is this just another way of denoting HSC inputs? I am looking at the manual (1766-UM001M-EN-P) and the only reference to the word fast in the entire thing (if the find feature is to be believed) is on page 16 when talking about the inputs themselves.

Thank you in advance.
Note: On the MicroLogix 1400 models which include 12 fast DC inputs, they are also referred to as high-speed DC inputs. This may help you in finding the relevant information within the User Manual.

If you go to Appendix A (Page 167), you should find the section -

Specifications for inputs

Under which you can find the information I believe you are looking for...

Inputs 0 through 11 (12 high-speed DC inputs)
Operating frequency - 0 Hz...100 kHz

Inputs 12 and higher (8 standard DC inputs)
Operating frequency - 0 Hz...1 kHz (scan time dependent)

So the definition of fast DC inputs in this case is 100 times faster than their standard DC inputs.

The high-speed DC inputs are handled by an on-board dedicated high-speed module whereas the standard DC inputs are not. This is why the high-speed DC inputs are not affected by the program scan time.

Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".

Last edited by Geospark; November 18th, 2018 at 01:05 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Micrologix 1400 and Citect gnash- LIVE PLC Questions And Answers 12 September 24th, 2014 02:46 AM
Modbus TCP communications with Micrologix 1400 H2Otbaker LIVE PLC Questions And Answers 6 April 13th, 2014 01:41 AM
Modbus tcp comm btw Micrologix 1400 and staubli robots s0787671 LIVE PLC Questions And Answers 11 March 10th, 2014 03:07 AM
Comunications between Micrologix 1400 and Sew Movidrive-B d4n1_g LIVE PLC Questions And Answers 0 October 31st, 2013 05:19 PM
MSG from MicroLogix 1400 to MicroLogix 1500 Marie1982 LIVE PLC Questions And Answers 3 September 3rd, 2010 11:46 PM


All times are GMT -5. The time now is 05:51 AM.


.