1734 aentr
Dear sirs ,
One of the 1756 EN2T MOdule communicated to three Ethernet adapters (1734 AENTR) . Normally During running condition every 10 mins Ethernet adapters point bus status and network status flashing red on all the three Ethernet adapters. Then again getting healthy automatically and cycle runs . Then again error came . Corrective action taken . 1. Network cable healthy condition 1. I replaced and shuffled adapters . 3.three Ethernet adapters powered by three seperate 24 v power supplies 4. I Replaced 1756 EN2T Need your advise to solve this issue . Thanks. |
![]() |
![]() |
#2 | |
Lifetime Supporting Member + Moderator
|
Welcome to the PLCTalk Forum community !
Quote:
I would examine the Ethernet switch carefully to see if it is also experiencing a disruption. Does this happen exactly every 10 minutes, or approximately every 10 minutes ? How long is the duration of the disruption ? |
|
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Feb 2018
Location: *******
Posts: 17
|
Hi sir . Thanks for your immediate reply . This issue not exactly every 10 minuets. Sometimes it’s running without issue for maximum 15 minutes. Sometimes issue appeared every 2 to 3 minuets.
The EN2T module connected to the AENT adapters through linear topology. ( without switch) Thanks. |
![]() |
![]() |
#4 |
Member
|
Are you certain all three AENT adapters have different IP addresses? And are they static IPs?
|
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Feb 2018
Location: *******
Posts: 17
|
Hi .
Sure . All the three Ethernet adapters having different IP address and Bootp - Dhcp disabled . |
![]() |
![]() |
#6 |
Member
|
How long has has the system been running?
Is there anything else connected to the network? If you look at the diagnostic screen for the 1756-EN2T, what errors are you seeing? |
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Feb 2018
Location: *******
Posts: 17
|
EN2T and 1734 AENTR ( 3 no’s ) . The system should run continuously to convey the product. Nothing else connected on the network.when the network status and point bus status flashing red the link down only shown in the EN2T card . The link led on the EN2T card not blinking that time .
|
![]() |
![]() |
#8 |
Member
|
Let me rephrase that. Is this a new system or one that has been running for awhile? Can you see the diagnostic screens on your PC, either on the web page or the module setup in RSlogix 5000 / Studio 5000?
|
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Feb 2018
Location: *******
Posts: 17
|
Actually this is not a new system . This system running for last 1.2 yrs . Now only we face this issue . In pc it shows connection timed out . In web page screen not able to find any error message .
|
![]() |
![]() |
#10 |
Member
|
When you look at the web page, check the diagnostic counters for collisions or errors. How long is the run of Ethernet cable between the devices and are they ran separate from power sources? You need to find out what changed.
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Flex 1794-AENT V AENTR | JohnCalderwood | LIVE PLC Questions And Answers | 0 | November 21st, 2017 10:41 AM |
Issue Moving 1734 AENT From One PLC to Another | Dave42 | LIVE PLC Questions And Answers | 10 | September 7th, 2016 01:26 PM |
1734 aentr | obi1987 | LIVE PLC Questions And Answers | 2 | March 31st, 2014 12:56 PM |
Aentr problem | buoanventura | LIVE PLC Questions And Answers | 1 | May 9th, 2012 01:45 PM |
1734 Aent and Security modules | Tarlo | LIVE PLC Questions And Answers | 5 | December 30th, 2011 12:37 PM |