Posts: 654
|
S7-1500 + CAN master
The main controller of a blower machine has died(it's a custom PC and the OEM is out of business).
This machine has 5 remote I/O's with CAN interface slave module (vipa 253-1CA01). The customer of the machine wants a Siemens plc probably an S7-1500. To keep cost down, we plan to keep the remote I/O's with CANopen, What are my options? Thanks for your thoughts
__________________
Optimist will tell you the glass is half-full; the pessimist, half-empty; and the engineer will tell you the glass is twice the size it needs to be |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Apr 2016
Location: From Canada - Living in Bulgaria
Posts: 1,985
|
Take a look at this, model HD67607-A1 Profinet/CanOpen gateway:
https://www.adfweb.com/home/products...pg=matrix_1_12 Keep in mind the ET200V from Vipa is obsolete. I would recommend replacing the CAN open network with Profinet and Profinet I/O when a bigger budget is available.
__________________
Automation Programmer PLC / HMI / SCADA / SQL New Systems, Modifications System Upgrades & Conversions Siemens EPROM & EEPROM Service ------------------------ Visit: contrologica.com Email: info@contrologica.com Last edited by sigmadelta; September 22nd, 2022 at 03:17 AM. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Mar 2022
Location: UK - The Norf
Posts: 246
|
The only CAN interface that I know of is for the S7-1200, unless you used something like an Anybus module.
I'd personally be costing up replacing those remote I/O's rather than trying to accommodate the CAN system, but I'm saying that without knowing either the machine or the customer and their budget. |
![]() |
![]() |
#4 | |
Lifetime Supporting Member + Moderator
|
There is the 6ES7137-6EA00-0BA0
Quote:
https://support.industry.siemens.com...view/109779316
__________________
Jesper ![]() NOTICE: JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm ! Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ |
|
![]() |
![]() |
#5 |
Lifetime Supporting Member + Moderator
|
Yeah. Such cost-cutting measures usually backfires in the long run.
__________________
Jesper ![]() NOTICE: JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm ! Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ |
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: Mar 2022
Location: UK - The Norf
Posts: 246
|
I stand corrected on the parts, didn't know that module was available.
Using the ET200SP CPU is also generally a much cheaper approach than the standard 1500. |
![]() |
![]() |
#7 | |
Member
![]() ![]() Join Date: Apr 2016
Location: From Canada - Living in Bulgaria
Posts: 1,985
|
Quote:
__________________
Automation Programmer PLC / HMI / SCADA / SQL New Systems, Modifications System Upgrades & Conversions Siemens EPROM & EEPROM Service ------------------------ Visit: contrologica.com Email: info@contrologica.com |
|
![]() |
![]() |
#8 |
Lifetime Supporting Member + Moderator
|
And 10 years from now, nobody including yourself can figure out how the special code for the CAN modules is working.
I am with the bite-the-bullet camp. Do the whole conversion to standard and up-to-date technology now, dont do it half now half later. The only reason for keeping the old IO hardware could that it is a large plant running 24/7 with almost no window to do the conversion. But 5 IO racks does not seem that large. edit: I have to admit that the current parts scarcity can be another reason for desperate measures.
__________________
Jesper ![]() NOTICE: JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm ! Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ |
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Mar 2010
Location: casablanca
Posts: 654
|
Thank you all for your valuable feedback.
I checked with vipa support team, they said there's a profibus interface module (253-1DP01) that can replace the CAN interface module, so it will be easy to speak to S7-1500 either via integrated profibus or with communication module. Also they said that the 200V System is active and will be supported for the next coming years. The reason for keeping those remote I/O's is not just the cost but also the long lead time to get new parts. there is another solution by using the SLIO system that can talk profinet. I see that there is vipausa.com and www.yaskawa.eu.com for vipa products, is there any difference between theme?
__________________
Optimist will tell you the glass is half-full; the pessimist, half-empty; and the engineer will tell you the glass is twice the size it needs to be |
![]() |
![]() |
#10 |
Lifetime Supporting Member + Moderator
|
Yaskawa owns VIPA. So they are the same.
Even though Profibus is more native than CAN to Siemens, for S7-1500 you would still have to add a Profibus CM, unless you chose a high-end CPU (which will be expensive) that has integrated Profibus. So with the extra Siemens CM plus 5 extra Vipa Profibus modules, it is again a lot of hassle and investment. Since you meantion the SLIO profinet is an option, I guess you are open to replacing the IO altogether. In that case I would go with any vendor that can provide Profinet IO at the moment. Siemens ET200SP is one of the worst for availability at the moment.
__________________
Jesper ![]() NOTICE: JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm ! Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ |
![]() |
![]() |
#11 |
Member
![]() ![]() Join Date: Mar 2010
Location: casablanca
Posts: 654
|
Thanks Jesper, I agree with you that ET200SP is one of the worst for availability at the moment, we have been quoted for 42 weeks lead time.
__________________
Optimist will tell you the glass is half-full; the pessimist, half-empty; and the engineer will tell you the glass is twice the size it needs to be |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
compact logix and s7 1500 communication | chandrapaul | LIVE PLC Questions And Answers | 1 | October 15th, 2019 12:40 AM |
Modbus TCP Connections - S7 1500 (TIA14) | ahuberee | LIVE PLC Questions And Answers | 0 | April 27th, 2017 12:39 AM |
S7 315-2DP / 341 Modbus Master with Multiple Slaves | richyr32gtr | LIVE PLC Questions And Answers | 1 | October 14th, 2009 12:05 AM |
s7 300 and 400 master slaving | moazzim | LIVE PLC Questions And Answers | 16 | April 10th, 2007 06:52 AM |
Need help S7 comm with MM440 & Simored DC Master | keahock | LIVE PLC Questions And Answers | 0 | December 4th, 2005 10:32 AM |