Old November 26th, 2011, 02:43 PM   #1
BMLLER6758
Member
Germany

BMLLER6758 is offline
 
Join Date: Aug 2006
Location: Kiel
Posts: 93
Panel Plus V5.10 Problems

Hi Guys,

I have a problem with an Application.

Factory Talk View ME 6.0 and 6.1
PVP 700 FRM 5.10
RSLinx Enterprise 5.40
Compact Logix L43S Version 18

While I create the Panel View Application it comes up with this Message:

*** Start RSLinx Enterprise Conversion Messages ***

WARNING: Unsupported device detected. Shortcut name = "PLC". Device name = "1768-L43S LOGIX5343 SAFETY".
Description: The system has detected that a device type that was not supported in the requested version is referenced by a shortcut.
If the system upon which this project is to be run has received a patch that adds support for this device type, then this situation
will not cause any problems. Otherwise runtime errors will be detected and logged by the target system when it attempts to communicate to that device.

*** End RSLinx Enterprise Conversion Messages ***

Validation completed with warnings. The runtime application has been created.
CAUTION: Running this application might produce errors at runtime.


Can anyone Help please
__________________
www.werner-kluge.com
Rockwell Solution Provider
  Reply With Quote
Old November 26th, 2011, 02:56 PM   #2
Kev77
Member
United States

Kev77 is offline
 
Kev77's Avatar
 
Join Date: Mar 2008
Location: Beaverton, Or
Posts: 407
Is the error when you create the app or the runtime app? If it is when you creating the runtime app, are you changing the version created from 6.1 to 5.1?
  Reply With Quote
Old November 26th, 2011, 06:15 PM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,694
I got the same warning with a v19 L43S controller and FTView 6.0 and 6.10 and have been able to safely ignore the warnings. RSLinx Enterprise has hard-coded hardware identification and has not caught up with the CompactLogix safety controllers.
__________________
- "Simpler is better, except when complicated looks really cool."
  Reply With Quote
Old November 27th, 2011, 07:12 AM   #4
BMLLER6758
Member
Germany

BMLLER6758 is offline
 
Join Date: Aug 2006
Location: Kiel
Posts: 93
Yes it happens while I create the runtime application

and Yes I set it to 5.10.

Maybe I have to install FT ME 5.10 ???

And Enterprise 5.10 ????
__________________
www.werner-kluge.com
Rockwell Solution Provider
  Reply With Quote
Old November 27th, 2011, 11:29 AM   #5
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 11,323
I would follow Ken's advice first (unless this is an extremely dangerous application) and ignore the error and test the system. What Ken is saying is that RSLinx Enterprise is not updated to include the newest hardware identification for the newest controllers. This doesn't mean it can't talk to them, it just means that it knows they aren't "on the list" of known controllers as far as RSLinx Enterprise is concerned. I seriously doubt that an older version of Enterprise would do you any good.
__________________
You've been taken, but you don't know it yet.
  Reply With Quote
Old November 27th, 2011, 11:44 AM   #6
curlyandshemp
Lifetime Supporting Member
Canada

curlyandshemp is offline
 
curlyandshemp's Avatar
 
Join Date: Jul 2005
Location: Toronto
Posts: 1,902
Quote:
Originally Posted by Ken Roach View Post
I got the same warning with a v19 L43S controller and FTView 6.0 and 6.10 and have been able to safely ignore the warnings. RSLinx Enterprise has hard-coded hardware identification and has not caught up with the CompactLogix safety controllers.
Same problem with the 1756-L7X series and PV Plus Compact.
__________________
Work to Ride,
Then Ride to Work

I would rather have a bottle in front of me..
than have a frontal lobotomy
  Reply With Quote
Old November 27th, 2011, 02:05 PM   #7
BMLLER6758
Member
Germany

BMLLER6758 is offline
 
Join Date: Aug 2006
Location: Kiel
Posts: 93
I already did it !

The application didnīt work, values from the PLC are only Questionmarks !!
__________________
www.werner-kluge.com
Rockwell Solution Provider
  Reply With Quote
Old November 27th, 2011, 02:22 PM   #8
Kev77
Member
United States

Kev77 is offline
 
Kev77's Avatar
 
Join Date: Mar 2008
Location: Beaverton, Or
Posts: 407
Are you browsing online for the tags? Doing it this way will narrow down the possibility that it is a maping problem. I'm sure that you know to copy the design route to the runtime as well. You might have two problems here. It might be as the Ken said and you have an Enterprise maping issue.
  Reply With Quote
Old November 27th, 2011, 02:27 PM   #9
BMLLER6758
Member
Germany

BMLLER6758 is offline
 
Join Date: Aug 2006
Location: Kiel
Posts: 93
Yes I route the Tags online.
__________________
www.werner-kluge.com
Rockwell Solution Provider
  Reply With Quote
Old November 27th, 2011, 02:31 PM   #10
Kev77
Member
United States

Kev77 is offline
 
Kev77's Avatar
 
Join Date: Mar 2008
Location: Beaverton, Or
Posts: 407
Not sure but would updating the firmware in the controller to version 19 help? Is it possible to upgrade the firmware in the PV as well?

Last edited by Kev77; November 27th, 2011 at 02:44 PM.
  Reply With Quote
Old November 27th, 2011, 03:16 PM   #11
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,694
Upgrades or firmware changes are unlikely to make a difference. As I mentioned, I have seen the exact same error message with the most up-to-date firmware and software for both the CompactLogix Safety controller (19.11) and FactoryTalk View / RSLinx Enterprise (6.10 / 5.40).

It's a warning, not a fault or error. My system is running properly with the L43S controller and two PV+ version 6.10 terminals.
  Reply With Quote
Old November 27th, 2011, 03:17 PM   #12
BMLLER6758
Member
Germany

BMLLER6758 is offline
 
Join Date: Aug 2006
Location: Kiel
Posts: 93
My customer want Version 18 in the PLC and 5.1 in the Panel.
__________________
www.werner-kluge.com
Rockwell Solution Provider
  Reply With Quote
Old November 27th, 2011, 03:52 PM   #13
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,694
Troubleshoot one problem at a time. The validation Warning is a good place to start, but the runtime errors are a more definite problem.

Test run the application on the development PC and examine the error messages that show up in the FactoryTalk View Studio diagnostic window.
  Reply With Quote
Old November 27th, 2011, 04:07 PM   #14
BMLLER6758
Member
Germany

BMLLER6758 is offline
 
Join Date: Aug 2006
Location: Kiel
Posts: 93
Absolutely no Error Message on the Dev. Laptop.

Working all fine...
__________________
www.werner-kluge.com
Rockwell Solution Provider
  Reply With Quote
Old November 27th, 2011, 04:12 PM   #15
curlyandshemp
Lifetime Supporting Member
Canada

curlyandshemp is offline
 
curlyandshemp's Avatar
 
Join Date: Jul 2005
Location: Toronto
Posts: 1,902
Quote:
Originally Posted by curlyandshemp View Post
Same problem with the 1756-L7X series and PV Plus Compact.
What I had to do was reconfigure the Runtime controller from L72 , as seen in the project browser:

to an L61
Attached Images
File Type: gif L61.gif (5.1 KB, 196 views)
File Type: gif L72.gif (4.6 KB, 179 views)
__________________
Work to Ride,
Then Ride to Work

I would rather have a bottle in front of me..
than have a frontal lobotomy
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
B&R Panel to PC Upload? alec24 LIVE PLC Questions And Answers 11 April 4th, 2020 06:52 AM
Process Panel programming - common question and LIVE PLC Questions And Answers 0 November 18th, 2009 12:55 PM
Panel View 1400E Comm Problems WireGuy1950 LIVE PLC Questions And Answers 0 April 29th, 2009 10:40 AM
Ab Panel View 300 Operator Panel ravirajesh01 LIVE PLC Questions And Answers 1 February 19th, 2007 01:53 PM
panel view 550 PERSPOLIS LIVE PLC Questions And Answers 3 June 7th, 2002 08:14 PM


All times are GMT -4. The time now is 03:49 PM.


.