Kinetix drive in stock forming ?

Kataeb

Member
Join Date
Jan 2007
Location
www.livelovelebanon.com
Posts
628
It will depend on how long the drives have been left without power, in general it is a good idea to power spare drives up at least once a year or even better every 6 months, if they have been in storage longer than that then it would be a good idea to use a lower voltage then increase it over time.
Reasons for forming:
the dielectric oxide layer starts to deteriorate if not powered for a time, this dielectric oxide layer reacts with the acidic electrolyte and the oxide layer starts to break down. When the dielectric layer starts to deteriorate, there will be a large leakage current that will flow when rated voltage is applied. This high leakage current flowing through the capacitor with the deteriorated dielectric can destroy the capacitors.
 
Rockwell is kind of weird about this. They recommend cap reforming on all of their "VFD" products but not on the K5700 platform. I never asked about the K6000 family or the K300/350.

I consider cap reforming like insurance. The chances of me ever using my homeowners insurance are pretty slim. But you can be sure if I ever drop the policy the thing will burn to the ground the next day. For what it costs versus leadtime to replace a drive, I would have the caps reformed.

Keith
 

Similar Topics

Hi, Again, a topic about Kinetix 5100 servo drives. The controller is L33ER. The servo drive are 2198-E1020-ERS with a TLP-115-200-DJMC2A. There...
Replies
0
Views
503
I am looking to upgrade some of our old Servo Drives to the newer kinetix 5700 style. currently we have 4 1394 axis that are all driven by 5kw...
Replies
1
Views
853
Hi All, I have a large servo indexer chassis that uses an AB servo and Kinetix 5500 drive. It seems logical to me to try to limit the amount of...
Replies
5
Views
2,075
I have a customer with a Kinetix 350 servo drive. They were having issues with the old servo motor so they replaced the servo motor with a new...
Replies
18
Views
8,240
We have a tissue Embosser which uses AB Kinetix 7000 drives and HPK servo motors. This particular fault concerns a 2099-BM07-S drive controlling a...