Using 1783 NATR with Siemens S7 PLCs.

PreLC

Member
Join Date
Apr 2019
Location
Mars
Posts
586
Hi,

I have S7 Profinet PLCs with local IP addresses in my plant. Can I use the 1783-NATR to configure a 1:1 NAT to get to the plant network?

Regards,
-PreLC
 
Update, it works! I had to add these to the "custom rule" section under Configuration>Network Address Translation. Otherwise I didn't get a reply back.

80 was for the webinterface, 102 for Profinet.

tcp/udp 102
tcp/udp 80

Regards,
-PreLC
 
I am currently trying to do the same thing, could you go into a little for detail on how you got this to work? I do not see a custom rule in the NATR setup. Thanks
 
I am currently trying to do the same thing, could you go into a little for detail on how you got this to work? I do not see a custom rule in the NATR setup. Thanks

Can you please share pictures of your NAT table? I'll try to guide you the best I can.
 
Yes, that is what I wanted.

If you have these rules, and the PLC still isn't communicating, have you set up the gateway on your S7 NIC to be the local address of the NAT? Is your NAT's gateway set to your plant's gateway address?

After this, can you open wireshark and see what error messages you get while using your client software(TIA/S7manager/Ignition etc)? The error messages would have port numbers, which would be used to see which ports further need to be opened up.

Regards,
-PreLC
 
Fixed! thanks

Thanks for your post PreLC!!

I just made what you recommended (Customs rules) a set Gateway Siemens PLC as the same as NAT (private network), and it is working.

Thanks for your help. đź“š :D
 
Thanks for your post PreLC!!

I just made what you recommended (Customs rules) a set Gateway Siemens PLC as the same as NAT (private network), and it is working.

Thanks for your help. đź“š :D

No problem man! If you discover something cool in the future, make a post too!
 

Similar Topics

Hello everyone, I'm working on a project that involves controlling an array of nozzles within a CNC environment, where the nozzles travel along a...
Replies
5
Views
128
Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
Replies
4
Views
132
Hi, Seeking consultation on an implementation matter, and have a question about Modicon Compact 984 communication through RS485: Three Modicon...
Replies
4
Views
106
Dear all, I don't know why setup of password became challenging and weird. After setting up the password and try to upload the ladder from the plc...
Replies
3
Views
93
Dear All, I need a sample PLC program to count the output pulse of a mass flow meter so that a specific amount of mass (for example 100gm)can be...
Replies
2
Views
82
Back
Top Bottom