FTV ME Screens for Multiple Identical Machines on one PLC

I am building a system that has three identical machines running in a single Logix PLC as separate programs: Cell1, Cell2, Cell3

There are going to be three screens that are used to run the machines.
The obvious way to do it is to build a screen for Cell1 and then clone it and replace instances of cell1 with cellx. However this is somewhat time consuming after each update.

I know you can pass the program name as a parameter when a screen is opened so I can add a parameter file for each screen specifying the cell number to use in the tags.

Is there a way to specify a global parameter that can be substituted to every screen so I only have to alter one parameter to change a screen from one cell to another after cloning?
  Reply With Quote
Old August 5th, 2022, 04:10 AM   #2
Phil Buchanan
Lifetime Supporting Member
United States

Phil Buchanan is offline
 
Phil Buchanan's Avatar
 
Join Date: Jun 2015
Location: Atlanta, Georgia
Posts: 616
This application would likely be better suited for FT View SE than ME.
__________________
PLC Boot Camp Training
VFD Training
HMI Training
Electrical License Prep Training
Motor Controls Training

http://www.KeyAutomationTraining.com
  Reply With Quote
Old August 5th, 2022, 08:03 AM   #3
celichi
Lifetime Supporting Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Greater Toronto Area
Posts: 394
Quote:
Originally Posted by Geoff White View Post
I am building a system that has three identical machines running in a single Logix PLC as separate programs: Cell1, Cell2, Cell3

There are going to be three screens that are used to run the machines.
The obvious way to do it is to build a screen for Cell1 and then clone it and replace instances of cell1 with cellx. However this is somewhat time consuming after each update.

I know you can pass the program name as a parameter when a screen is opened so I can add a parameter file for each screen specifying the cell number to use in the tags.

Is there a way to specify a global parameter that can be substituted to every screen so I only have to alter one parameter to change a screen from one cell to another after cloning?
How many tags do you have on each screen?

Depending on how you do your tagging, CTRL-R does a tag substitution on what you have selected.



From the Manual...

(Rockwell Automation Publication VIEWME-UM004Q-EN-E - March 2022)

Use these global connections to replace tag placeholders in displays that use
parameters when they open:
Parameter file identifies the parameter file for the display being
opened remotely.
Use Parameter List notifies the application that a parameter list is
to be used to provide the parameters to the display being opened
remotely.
Parameter Tag #1-10 the tag values assigned to these global
connections will replace the tag placeholders on the display being
opened remotely

Chapter 25, pages 401-415
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
FTV ME not seeing tags from PLC HoldenC LIVE PLC Questions And Answers 16 June 10th, 2021 04:08 PM
rslogix 5000 - newbie doubt kuppe35 LIVE PLC Questions And Answers 10 February 3rd, 2021 10:53 AM
FTV SE Multiple Screens ian.smith7 LIVE PLC Questions And Answers 8 April 13th, 2018 02:42 PM
Mitsubishi problem gunther LIVE PLC Questions And Answers 11 June 17th, 2006 10:01 AM
Real World Problem Vietnam Bob LIVE PLC Questions And Answers 8 November 23rd, 2002 03:03 PM


All times are GMT -4. The time now is 07:50 AM.


.