Eurotherm 584s Drive :

rohanlyn

Member
Join Date
Aug 2011
Location
uae
Posts
6
Eurotherm 584S Variable frequency drive (4kW} tripped with 4kW motor( pump application ) while running at 32HZ.
trip alarm was DC LINK OVER VOLTAGE.
Please provide solution
 
Eurotherm 584s

I increased ramp down time.
Checked input voltage using fluke Analyzer .
Not much variation ( 234- 238V)with Neutral .
The drive is tripping after 2 ,3 hours .
since last month this fault appears .
 
no .
What will be the rating of the brake resistor ?
Is there any formula to calculate brake resistor value ?
 
First, is drive running in V/Hz or vector mode?
Second, does the drive fault when running at steady speed or when decellerating?
Third, you gave us voltage to ground. What is the phase-to-phase voltage and is the power source referenced to ground in any way or is it floating.
Fourth, is the drive CE rated? If it is, there will be a CE mark on it, probably on its ID plate.
 

Similar Topics

Saludos amigos. Tengo una impresora comexi modelo FS1500, la impresora usa intouch 7 en Windows 2000, viene con un PLC Omron C200HS, también usa...
Replies
6
Views
1,088
I'm just needed the iTools to configure the settings using RS485. Unless I read it wrong it is FREE for just that purpose. I went on Eurotherm...
Replies
1
Views
587
We are changing from an old Eurotherm drive to an AB753 and I have a few questions. Seems like the 753 has less I/O's on Port 0 in comparison to...
Replies
2
Views
1,094
Dear all, we have a couple of SSD 637 servo drives that need to communicate trough easyrider. On the parker website you can download easyrider...
Replies
0
Views
507
I am trying to get a Mitsubishi GT2715 HMI to read and write from a Eurotherm 3508 controller using 4 Wire RS485 Mobus RTU communications. The...
Replies
3
Views
1,292
Back
Top Bottom