Any ideas on who to convert 0-30v to 4-20mA or 0-10v I know I can use a potential divider with a few resistors but need something that can be "Bought" and rail mounted rather than "made"
Need t get a 24v Battery condition signal into a PLC for monitoring over profibus. Only have spare 4-20mA analog inputs. |
![]() |
![]() |
#2 |
Lifetime Supporting Member + Moderator
|
Just a simple resistor would get your 30v to 10v, not sure of the size you would need but I go from 0-24vdc to 0-10vdc all the time with a resistor, the size depends on what you are connecting to, mine range from 75 ohm to 300k
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways |
![]() |
![]() |
#3 |
Supporting Member
|
Not sure if loop powering them would be possible in your situation, but maybe look into Acromag's TT238. Multiple range (+/- 75VDC range in your case) DC voltage input, 4-20mA output.
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Oct 2004
Location: Midlands
Posts: 1,415
|
Have a look at these:
https://www.spectra-displays.co.uk/s...gnal-converter |
![]() |
![]() |
#5 |
Member
|
Go to this voltage divider calculator.
Need to split 30V into 20V & 10V, then watch the 0-10V side. Since it's only a signal only need to divide 1 watt or 0.01 amps.
__________________
Never underestimate the quality of idiots that will be running your machines ![]() http://aabeck.com |
![]() |
![]() |
#6 |
Member
|
|
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Sep 2015
Location: Alberta
Posts: 76
|
I have a Weidmuller 1481970000 here that would do just that. Weidmuller 1481970000
|
![]() |
![]() |
#8 |
Lifetime Supporting Member
![]() ![]() Join Date: Jul 2012
Location: IN
Posts: 659
|
Automation Direct has 0-50VDC in 4-20MA out
https://www.automationdirect.com/adc.../vdct050-42-24 |
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Mar 2009
Location: ST CYrus
Posts: 49
|
Cheers got a solution
|
![]() |
![]() |
#10 |
Lifetime Supporting Member + Moderator
|
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways |
![]() |
![]() |
#11 |
Member
![]() ![]() Join Date: Jan 2008
Location: Belgrade
Posts: 276
|
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
RSLogix 500 - I/O mapping question | toads | LIVE PLC Questions And Answers | 8 | September 25th, 2019 12:40 PM |
Analog Input location for PLC5/20 | sboudreau | LIVE PLC Questions And Answers | 3 | March 28th, 2012 03:47 PM |
1762-1F4 Analog Input | toarts | LIVE PLC Questions And Answers | 2 | October 20th, 2010 05:04 PM |
Scalling for analog input module - SLC 5/04 | ckchew666 | LIVE PLC Questions And Answers | 1 | May 15th, 2008 10:31 AM |
Analog Input to Analog Output | rawtalent | LIVE PLC Questions And Answers | 6 | March 22nd, 2005 05:02 AM |