If a VFD is already classified for single phase input, does it still need to be de-rated? Will the motor(specs) shown below, work with the listed VFD specs or do I need to go with a VFD with higher Amp rating? Trying to avoid a step-up transformer and I haven't come across a VFD rated for higher amp rating than what is shown below that can work off a singe phase 115VAC supply.


Thanks.

1Phase VFD.png
 
it should work no derating necessary
from what I see it has a voltage doubler built in
120 1Ph supply with 230V 3Ph output to the motor
what band is it it looks like it may be Yaskawa
 
it should work no derating necessary
from what I see it has a voltage doubler built in
120 1Ph supply with 230V 3Ph output to the motor
what band is it it looks like it may be Yaskawa

I think that’s a Weg part number.

But correct, no de-rating necessary because it is already rated for single phase input. 1-1/2 HP is the upper limit of 120V input, because beyond that the voltage doubler circuit becomes more expensive than a transformer.
 

Similar Topics

Hi all. Will something like this work on a VFD output ? Carlo Gavazzi E83-2050 The VFD output frequency will be between 45-55 Hz. I know that its...
Replies
6
Views
2,127
Hi all, Client with a pretty much brand new AB Powerflex VFD starting throwing Fault 17: Input Phase Loss this afternoon. Started doing some...
Replies
6
Views
9,465
I know this has come up many times but I've yet to hear a good way to deal with the vfd issue. Here's where I am. I have a very old Haas milling...
Replies
31
Views
12,048
I have been looking at a couple of power tools that have a 220v 3 phase motor. I was wanting to avoid having to install a rotary converter. But I...
Replies
7
Views
2,208
Hi all, I'm in the search for a 1 phase in, 1 phase out VFD, 110 VAC, 1/4 hp. Any recommendations? It would be great if it has a keypad that can...
Replies
6
Views
2,071
Back
Top Bottom