PowerFlex 525 - can you access the parameters from a MicroLogix 1400 & CompactLogix

Good Morning ,

I have a separate stand alone machine that I want to change its conveyor from another machine via Ethernet. Can I create this drive in the Ethernet tree in a Controllogix as a new module , and have it create the controller tags ? If so can I write to the command frequency, and possibly override the MicroLogix 1400 commands ? Or I may just cancel out that speed reference from the MicroLogix 1400.

Thank in advance ,
 
Yes, you can. Your best bet is to put the drive in the ControlLogix tree and set up ethernet comms to READ the different VFD commands from the ML1400. You can then use logic in the controllogix to override the micrologix commands if need be.

The micrologix can control the drive via ethernet directly but is very limited in the types of commands, and its pretty janky in general.
 

Similar Topics

Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
228
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
Replies
2
Views
233
New to vfds. I put in parameters. IP, but I get ethernet flashing and link solid. What did I do wrong?
Replies
9
Views
469
Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
Replies
4
Views
224
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
Replies
6
Views
294
Back
Top Bottom