Old July 10th, 2015, 11:37 AM   #1
Narlin
Lifetime Supporting Member
United States

Narlin is offline
 
Narlin's Avatar
 
Join Date: Mar 2010
Location: phoenix
Posts: 320
1769-OF4 issues

I am having trouble scaling a 1769-OF4. By &by, I do these several times a year and this is the 1st one that is giving me this issue. What I want is 4mA for 0% input and 20 mA for 100% input to PID. Card seems to be working. Obviously I am not.

On the PID setup Scaling Screen:
PV Unscaled Max 100.0 Eng. Units Max 100.0
Unscaled Min 0.0 Eng. Units Min 0.0
.
CV Max 100% No Tieback
CV Min 0%
.
Software manual is checked and I am operating in Manual.
.
Card Configuation:
1769-OF4 4 Channel Current/Voltage Analog Output Series A Rev 1.1



4 different setups with Results:

1st Result
Channel 0 Enable (Check)
Output Range 4mA to 20mA
Data Format= Percent Range
Limits: High 10625 Low -500 (Latch Limit Alarms not checked)

Input to PID 0% Output from Card 4.0 mA
Input to PID 25% Output from Card 12.0 mA
Input to PID 50% Output from Card 20mA (why ???????)

2nd Result
Channel 0 Enable (Check)
Output Range 4mA to 20mA
Data Format= Scaled for PID
Limits: High 17407 Low -819 (Latch Limit Alarms not checked)

Input to PID 0% Output from Card 4.0 mA
Input to PID 25% Output from Card 8.88 mA
Input to PID 50% Output from Card 13.76mA
Input to PID 82.0% Output from Card 20mA (why ??????)
Input to PID >82%, no change from whatever it was reading

3rd Result
Channel 0 Enable (Check)
Output Range 4mA to 20mA
Data Format= Engineering Units
Limits: High 21000 Low 3200 (Latch Limit Alarms not checked)

Input to PID 0% Output from Card 3.2 mA
Input to PID 25% Output from Card 5.0 mA
Input to PID 50% Output from Card 10.0 mA
Input to PID 75.0% Output from Card 15.0mA
Input to PID 85.5% Output from Card 17.31%
Input to PID >85.5%, no change from whatever it was reading
(canít get to 20mA here)

4th Result
1st Result
Channel 0 Enable (Check)
Output Range 4mA to 20mA
Data Format= Raw Proportional
Limits: High 32767 Low -32767 (Latch Limit Alarms not checked)

Input to PID 0% Output from Card 12.09 mA
Input to PID 25% Output from Card 13.45 mA
Input to PID 50% Output from Card 14.81mA
Input to PID 75% Output from Card 16.16 mA
Input to PID 86.7% Output from Card 16.80 mA
Any higher results in no change, no matter what the prior reading.
  Reply With Quote
Old July 10th, 2015, 12:26 PM   #2
Narlin
Lifetime Supporting Member
United States

Narlin is offline
 
Narlin's Avatar
 
Join Date: Mar 2010
Location: phoenix
Posts: 320
Fixed it.
There was some additional program scaling (a 3 rung program so three chances to mess up !)
that was limiting output. Best part, it was fixed on the OIT screen - no additional programming involved.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Turck RFID Issues / Help? AbjectControl LIVE PLC Questions And Answers 6 September 4th, 2015 01:31 AM
1769 OA16 Changeout questions sparkytex LIVE PLC Questions And Answers 7 October 18th, 2013 05:16 PM
WinCC 2008 Flexible issues JOLTRON LIVE PLC Questions And Answers 3 March 25th, 2009 05:45 PM
Lost Ethernet option link from a 1769 L35E captain_fracasse LIVE PLC Questions And Answers 7 October 2nd, 2008 02:23 PM
Ml1500, 1769 If4i Thomas Franklin LIVE PLC Questions And Answers 2 December 1st, 2006 04:04 PM


All times are GMT -5. The time now is 04:54 AM.


.