I have a Micrologix 1100 Series B. I cant get my DF1 driver to communicate with it. I have current RSLinx and good cable. Tried it out on a ML1400 and configured immediately. ML1100 was sitting on the shelf for years and the battery is dead. Program probably lost too. It is faulted. Shall I declare time of death?
Old May 15th, 2018, 09:01 AM   #2
RobertB
United States
RobertB is offline
RobertB's Avatar
Also... fault screen says, "Major Error" Code=0187h
Old May 15th, 2018, 09:04 AM   #3
geniusintraining
United States
geniusintraining is offline
geniusintraining's Avatar
See if you can use Bootp via the Ethernet port, then clear the memory and try DF1 again
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
Old May 15th, 2018, 09:49 AM   #4
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
Is the fault LED solid or flashing?
The error code 0187h indicates that the PLC is configured for a module in slot one that does not match what is actually there. There is a good chance that the PLC is just fine, just not happy with what its brain says about its body.
It is also quite possible the channel configuration is so different from your RSLinx driver configuration that it simply doesn't show up. I would definitely try Ethernet since you should be able to at least view the configured IP address from the LCD on the PLC.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
Old May 15th, 2018, 11:54 AM   #5
LoganB
United States
LoganB is offline
Code 187! Murder Death Kill!
(Anyone get the reference?)
__________________
Present: Controls Engineer
Future: Skynet Engineer
Old May 15th, 2018, 12:34 PM   #6
Dravik
United States
Dravik is offline
Frigging seashells.
Old May 15th, 2018, 01:56 PM   #7
geniusintraining
United States
Quote:
Originally Posted by Dravik View Post
Frigging seashells.
So I got the 187... but I have no idea what your talking about
__________________
Old May 15th, 2018, 02:45 PM   #8
Dravik
United States
Dravik is offline
Quote:
"he doesn't know how to use the 3 seashells"
Old May 15th, 2018, 02:48 PM   #9
keithkyll
United States
keithkyll is offline
If I remember correctly, the 1100 has a pushbutton to set the RS232 channel to default settings. You have to do this if you have an HMI, because the HMI and RS Linx have different settings.
Old May 15th, 2018, 02:56 PM   #10
RobertB
United States
RobertB is offline
RobertB's Avatar
Thank you all for your advise. In the settings, you can DISABLE DF1 comms. (Never saw such before) The previous programmer DISABLED DF1 comms.
Also, despite shelf time, it still had it's i/o configuration. Since it wasn't mated with its previous cards, it declared an 0817h error.
I went into ADV settings, ENABLED the DF1 comms, and downloaded the new configuration and program.
I am up an running now.
Old May 16th, 2018, 09:17 AM   #11
alive15
United States
alive15 is offline
Robert, to clarify what you did, you are saying you went into the advance settings of the card on the PLC program itself or in RS Linx?
Old May 16th, 2018, 09:25 AM   #12
geniusintraining
United States
Quote:
The settings are in RSLogix in the tree, there are communication settings and you can configure the ports there
__________________
Old May 16th, 2018, 09:52 AM   #13
alive15
United States
alive15 is offline
Talking
Ok great, thanks.
Old May 16th, 2018, 10:08 AM   #14
forqnc
United States
forqnc is offline
Just to add this small info. I am new to the MicroLogix series. Got a brand new 1400 (this morning) to program for a customer. Found I had to go to the Advance set and enable the DCOMM through keys on the PLC to be able to communicate.
Old May 16th, 2018, 10:38 AM   #15
RobertB
United States
RobertB is offline
RobertB's Avatar
I changed a setting IN THE PLC. Why AB even put this option into a PLC... I don't know.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
weirdness ... a MicroLogix 1100 wearing a 1794-AENT Tee-Shirt ... Ron Beaufort LIVE PLC Questions And Answers 12 August 1st, 2016 06:34 PM
MSG Instructions, MicroLogix 1100 to CompactLogix 1769-L32E kmlongee LIVE PLC Questions And Answers 4 May 2nd, 2016 06:54 PM
Micrologix 1100 to Micrologix 1100 Communications emomorales LIVE PLC Questions And Answers 4 February 5th, 2015 11:45 AM
MicroLogix 1100 EEPROM Failure bfoss LIVE PLC Questions And Answers 2 May 3rd, 2010 02:03 PM
Micrologix 1100 using an older OPC server to Labview... frenchy LIVE PLC Questions And Answers 3 November 17th, 2008 03:17 PM