PanelViewplus F/W Ver 8 screen resolution & boot up issue

Eoghan

Member
Join Date
Oct 2013
Location
Galway
Posts
37
Hi,
Just upgrade firmware on touchscreen panel view plus 6 1250 from 7 to 8.
Cursor is off the mark by about 2 inches!!
How do I force screen to re-calibrate itself?
And how do I cause FTView F/W 8 to boot into Windows and not ME application at bootup?
Thanks,
E
 
This is actually pretty common; firmware upgrades delete the screen calibration data.

There's a screen calibration process in the FTView ME project configuration menus. Plug in a USB mouse and you'll be able to navigate, then use the screen itself to touch the spots it indicates.

As for starting to Windows and not FTView ME... I think you have to get into the desktop access section of the FTView ME project configuration menus (you'll need to set a password somewhere along the way), then select whether to start FTView ME or not.
 
This is actually pretty common; firmware upgrades delete the screen calibration data.

There's a screen calibration process in the FTView ME project configuration menus. Plug in a USB mouse and you'll be able to navigate, then use the screen itself to touch the spots it indicates.

As for starting to Windows and not FTView ME... I think you have to get into the desktop access section of the FTView ME project configuration menus (you'll need to set a password somewhere along the way), then select whether to start FTView ME or not.
Thanks.
Ended up programing a 'Shutdown' button in one of HMI screens - allows me get back into PP+ config page.
 

Similar Topics

Hello, Have same FTView 6 programmed application running on PV+ Firmware 3.1 HMI and running on PV+ Firmware 5.1 HMI. Both connect to ML1000...
Replies
5
Views
1,599
I'm having problems with a PanelViewPlus over a VPN. I have a road warrior account setup on the main vpn server and a tunnel between the main...
Replies
5
Views
3,587
Hello Everyone, I am setting up an Information message in FactoryTalkView ME. I'm just using the default information display. I want to make it...
Replies
4
Views
843
Hello to the community, I am new to Rockwell and I have a small problem with a PvP1000(2711P). Some buttons in the same screen are not...
Replies
4
Views
2,326
Hello, I have a PV+ 1000 that I am unable to access the config screen on. All I want to do is upload the .mer that is currently running. I tried...
Replies
21
Views
4,895
Back
Top Bottom