Old July 25th, 2007, 02:19 AM   #1
PLC_talk
Member
India

PLC_talk is offline
 
Join Date: Oct 2006
Location: p
Posts: 50
SLC 500 PID problem

Hello ALL,
I am facing a problem while executing the PID instruction. As soon as the Processor is put in Run mode the CPU goes to fault indicating PID fault. If the instruction is deleted then the rest of the program works fine.
I have set the parameters as follows -
Kc-0.5, Ti- 0.1, Td- 0.0 , Loop update - 0.2 , Mode- Sp-PV, Control - Auto, Time mode - STI, SP MAx- 16383, SP min 0, CV Max - 100, CV MIn -0
In the processor status-STI tab S30= 20, S31 = 7, s:2/1 = 1

Is the S31 related to the Program file where the PID instruction is placed? Mine is in File 7.
In Run mode my Loop update time gets reset to 0.

I am not able to find the exact cause of this, so would appreciate any pointers in right direction.

Thanks,
  Reply With Quote
Old July 25th, 2007, 04:20 AM   #2
Myles
Member
Scotland

Myles is offline
 
Join Date: Jul 2007
Location: edinburgh
Posts: 175
Change the timed mode to TIMED rather than STI. I had this problem before and that sorted it.
  Reply With Quote
Old July 25th, 2007, 12:41 PM   #3
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,617
Greetings PLC talk ...



Quote:
In Run mode my Loop update time gets reset to 0.


based on this statement, I’d bet (more than pocket change) that you have a “memory overlap” situation ... specifically, something else beside your PID might also be using part of the PID’s 23-word memory block ... that “something else” could be another ladder logic instruction - or it might be an HMI/SCADA station that’s writing into that memory area ...







in the example above, the 23 words starting at N10:0 are dedicated to the PID ... so N10:0 through (and including) N10:22 should not be “written into” except very carefully to change the setpoint, etc. ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp - Retired | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.

  Reply With Quote
Old July 26th, 2007, 12:28 AM   #4
PLC_talk
Member
India

PLC_talk is offline
 
Join Date: Oct 2006
Location: p
Posts: 50
Thanks Ron / Myles,
I will reassign some other N file & test it. BTW the error I am getting is " An invalid value is being used for the PID instruction parameter" . Also in the RUN mode the MODE gets set to TIMED & loop update to 0.

Regards,
  Reply With Quote
Old July 26th, 2007, 09:53 AM   #5
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,318
Post your code (.RSS file)zip it then post it. If you can.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old July 26th, 2007, 10:08 AM   #6
mgvol
Member
United States

mgvol is offline
 
mgvol's Avatar
 
Join Date: Dec 2004
Location: Knoxville, TN
Posts: 746
What is the value used for the PV scaled to? The PV must be scaled to a value between 0 and 16383; anything above/below this will cause that type of fault. If it is scaled to that value, see if there is any logic in place to prevent under/over-ranging the PV address. Even if scaled properly (0-16383), if the device providing the PV value (transmitter, etc.) fails, you could get a high or low out of range value.
  Reply With Quote
Old July 29th, 2007, 11:53 PM   #7
PLC_talk
Member
India

PLC_talk is offline
 
Join Date: Oct 2006
Location: p
Posts: 50
Hello,
Thanks for all the inputs.I was able to solve the problem by setting the loop scan to 1.2.
  Reply With Quote
Old July 30th, 2007, 11:06 AM   #8
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,617
Greetings PLC_talk ...



we’re glad that you’ve found a solution - and if you’re happy, then we’re happy ...



but ...



there has to be more to it than just setting your “loop scan” (Loop Update?) to 1.2 ... in your first post you mentioned that you were setting the Loop Update to 0.2 ... and then you said:



Quote:
In Run mode my Loop update time gets reset to 0.




so the question remains: if the original setting of 0.2 was being reset to 0, then why is the new 1.2 setting not being reset to 0 also? ...



but if it’s working and you’re satisfied, then I suppose that’s a happy ending ... still, I’ve got a hunch that you did a little bit more to get this system working than simply changing the Loop Update setting from 0.2 to 1.2 ...



anyway ... good luck with the rest of your project ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp - Retired | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.

  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC 500/RSLogix 500 Communications kerch LIVE PLC Questions And Answers 25 October 15th, 2006 01:19 AM
A/b Slc 500 Johnny Rotten LIVE PLC Questions And Answers 11 September 29th, 2005 12:27 AM