S7 redundancy hangups!

Hello All,
First I tried browsing all the earlier posts to check for some solution, but can't find it.. so here is the problem

Situation 1 - S7-400H system in redundant mode, Works fine when both CPUs are in RUN. If the standby CPU is taken to STOP & then turned back to Run mode then it doesnot go back to RUN & the system runs in SOLO mode. Have to shutdown both the CPUs & turn them ON again to get back redundant running.
Situation 2 - Both CPUs working in RUN mode & any changes to Master CPU ladder, then again, if the standby CPU is taken to STOP & then turned back to Run mode then it doesnot go back to RUN & the system runs in SOLO mode. Have to shutdown both the CPUs & turn them ON again to get back redundant running.

Am I doing any procedural mistake or its some programming error?
It bugs me that as per manual the ladder shoulg get transfered from master to standby if the standby CPU is turned from RUN-STOP-RUN mode.


Any words of wisdom?

Thanks,
  Reply With Quote
Old January 30th, 2007, 07:27 AM   #2
PLC_talk
Member
India

PLC_talk is offline
 
Join Date: Oct 2006
Location: p
Posts: 50
Does anyone know which Siemens manual tells about the Event IDs & errors in the Diagnostic buffer.
One stupid question - There is a S7 software redundancy manual. Is it a strict no-no to refer if I am using s7400H H/W redundancy?
Some of the prerequisites in it are confusing me; e.g. Only IEC timers allowed , S5 timers will not work in redundacy system.

Any suggestions???
  Reply With Quote
Old January 30th, 2007, 09:57 AM   #3
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 14,232
Quote:
Originally Posted by PLC_talk
One stupid question - There is a S7 software redundancy manual. Is it a strict no-no to refer if I am using s7400H H/W redundancy?
I have no experience with redundancy, but I would definitely ignore that manual and find the correct one.
__________________
Jesper
See my profile interests for Q&A
  Reply With Quote
Old January 30th, 2007, 10:35 AM   #4
Marsupilami
Member
Belgium

Marsupilami is offline
 
Marsupilami's Avatar
 
Join Date: Jul 2004
Posts: 124
Thats strange behaviour. we have a S7-400H system running and we never saw such a thing.

As for an online change, we dont need to stop the standby CPU to copy the change to the standby CPU. when you download the change it is immediatly copied to both the CPU's.

the only limitation is that you cant download when Rack 0 is not reachable.

Regards,

Marsupilami
__________________
Dont take life too seriously you wont survive it anyway
  Reply With Quote
Old January 30th, 2007, 01:07 PM   #5
sylent
Member
United States

sylent is offline
 
sylent's Avatar
 
Join Date: Apr 2006
Location: San Diego
Posts: 88
sync

Have had some experience with 400H's and usually if you are monitoring one such as in a VAT or ladder it will not let them sync up fully - or it sees it as a difference so if you power down the stand by and power it back up - they won't sync until everyone stops monitoring and you put the standby from stop to run. Also if you have a programming cable attached to one and not the other it will be fine if they are both running, but if one stops they won't be able to sync again because it sees a difference between the two - or at least this is my understanding of this behavior... Other than these few quirks they've been great.
  Reply With Quote
Old January 30th, 2007, 11:26 PM   #6
PLC_talk
Member
India

PLC_talk is offline
 
Join Date: Oct 2006
Location: p
Posts: 50
Quote:
Originally Posted by sylent
Also if you have a programming cable attached to one and not the other it will be fine if they are both running, but if one stops they won't be able to sync again because it sees a difference between the two - or at least this is my understanding of this behavior... Other than these few quirks they've been great.
Sylent, Thanks for your suggestion. This is one thing I hadn't tried nor thought of!
Will let you know if it works this way.
Presently I am getting errors in diagnostic buffers as - #49A4 - Inconsistency in configuration data , & #530DSDB error.

Thanks
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens S5 and S7 Dual Masters for Profibus daveswerld LIVE PLC Questions And Answers 15 December 16th, 2008 03:15 AM
Redundancy on S7 300 PLCs Eduardo Pelegrin LIVE PLC Questions And Answers 11 August 18th, 2008 04:58 AM
S7 400 CP 443 Redundancy teh LIVE PLC Questions And Answers 4 August 20th, 2006 04:17 PM
New to S7 and MP270 NetMan LIVE PLC Questions And Answers 19 July 25th, 2006 11:38 AM
S7 300 And Software Redundancy sanjay_snj LIVE PLC Questions And Answers 0 May 16th, 2005 01:20 PM


All times are GMT -4. The time now is 09:50 PM.


.