Modbus TCP - ControlLogix <> S7
sthompson
Jan 2007
Vernon, BC
1,852
We have a need to communicate between a ControlLogix PLC and an S7 PLC on Ethernet. Modbus TCP has been suggested, but I am looking for any suggestions. Ethernet is preferred, because we already have an existing PLC Ethernet Network we can use.
We are looking at an Ethernet Card in the S7 Rack and another Card in the ControlLogix Rack.
We need to exchange Digital and Real/Float Data.
Is Modbus TCP the best option, any other options?
If Modbus TCP is the best option, any recommended Cards?
I appreciate any help and suggestions.
Stu....
Do you have to do this one a shoestring budget, or can you spend a little money for simplicity/reliability ?
The users who have installed them say nothing but good things about the OLDI/Prosoft Industrial Message Manager module:
http://www.prosoft-technology.com/content/view/full/13843
I think the Forum favorite would be the Red Lion DataStation Plus.
http://www.redlion.net/Products/HumanMachineInterface/DataStationPlus/DataStationPlus.html
The "DSPLE" model is the basic protocol bridge without a virtual HMI, so it's a little less expensive but uses the same Crimson 3 software.
You'd use the A-B "Native Tag Addressing" driver to communicate with ControlLogix over EtherNet/IP.
Crimson 3 has two Siemens S7-related Ethernet drivers: "Siemens S7-300/400 TCP/IP Master", and "Siemens CP243 via ISO TCP/IP Master".
Hello all, I was wondering if you clever people could help me, please. In the past I have used a standalone L33ER CompactLogix PLC with the...
1,522
I am working on a project, inside an AB CLX, I implemented the Modbus TCP Client AOI published on AB website, to interreact with a Modbus ASCII...
3,549
I am not very experienced in Rockwell PLCs and have run into a small problem, so I could do with a little bit of help. We have a redundant...
2,518
Hello All, I'm looking for the Coles notes on how to inferface a Modbus TCP device (compressor controller) with a Logix 1756 L72 running V24...
5,883
Hi all, I'm working on a wastewater plant where I have a ControlLogix PLC as the master PLC, alongside three packaged systems that are being...
3,860