I have a page in my logix5000 code that is there for the sole purpose of letting me see every command, status, and sequence bits + a few position integers. Is this bad practice to have these kind of pages as tags can be readily viewed. I don't call the routine with JSR so I don't think it will effect scan time?

Thank you,
Darkzadow
 
I don't think it's a bad idea at all. It's nice information for troubleshooting.

Sometimes I put important information at the top of a routine with a [NOP] instruction at the end (so it doesn't scan).
 
The [NOP] at the top of a routine sounds great. Relevant information with relevant location. I think ill try moving some of the indicators there as well.
 
Sometimes I use a rung with a comment and [NOP] in different places in a routine to group logic together.
Speaking of comments, if you are doing this make sure to have a comment that says there is no JSR and that it is for status, so some future programmer doesn't have to figure out why you have code that serves no (functional) purpose.
 
Darkzadow
For me this is common practice for example I like to group all the digital IO from a drive in the first few rungs of a drive file so when I open the file I know if it's running/ready or faulted. Also I group together different variables of a process in a run kinda like a mini VAT in Step7. I do try to to comment these rungs..
I sometimes stick a AFI in at the begining of the rung so it is not evaluated (although AFI's left in the program seems to offend some.)
 

Similar Topics

Hi everyone i have a customer, who wants to show an alarm on the machine, if the I/O forces are enabled and set, on at ControlLogix L81E with...
Replies
3
Views
235
I have a password protected Siemens ET200SP PLC, with 'Permit access with PUT/GET communication from remote partner' option disabled. Is there...
Replies
1
Views
452
On this project, the operator's asked me to add an LED onto the cabinet of the PLC enclosure, such that the LED illuminates when the PLC's...
Replies
13
Views
1,046
Looking for a way to export PLC status to Kepware ultimately. In Rockwell we can do a GSV and get a lot of information about the PLC. Is there...
Replies
1
Views
1,567
Hey guys, We are using a compactlogic 5069-L33 with an Panelview in our project. Currently busy with some diagnostics displays of the PLC and...
Replies
4
Views
1,804
Back
Top Bottom