FactotyTalk View ME acknowledge alarm

pr_wainwright

Member
Join Date
Jun 2011
Location
Stockton on Tees
Posts
109
Hi,
I have a client who wishes to be able to acknowledge individual alarms on a PanelView Plus 6 HMI. E.g. an alarm comes in & the associated graphic flashes red. Once the alarm is acknowledged the graphic stops flashing but remains red. Is there some way i can detect if an individual alarm has been acknowledged in my animation script? E.g. mytag.ack / mytag.unack?

Thanks
Paul.
 
Hi Paul

I know you can show ack and unack works in the alarm history and you can assign a color to each but I am not are about getting the back round color to flash. If you look in the alarm history and then look at display I think there you selected what you woils like to display.
You could create your own alarm display of you really wanted to but it would be a lot of work .

Donnchadh
 
go to Alarm setup and look under the advanced tab you will Tags for use there. Assign your tag to the ones you want to use and write code in plc to to determine the difference. Once you get to the advance tab use the help button to get info on tags. Quickest way to the location in the help files.

You can also set individual tags for alarms on the trigger page by selecting the trigger and filling out tag info. Again click help for definition from that page.
 
Last edited:

Similar Topics

Hello fellow wirenuts, I am looking to find the P.B. touch indicator option on version 13.00 and failing. It has been a year or so since I last...
Replies
4
Views
115
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
129
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
64
Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
1
Views
75
Hello Friends I have 2 languages in my app, en-US, es-MX. I need to send CurrentLanguage to PLC, I am trying with Macro in Global Connections...
Replies
5
Views
165
Back
Top Bottom