Hi,

Last night, I did a station upload from a 314C CPU. I downloaded these blocks in a S7-315 CPU, but it refuses to download FC10, FB3, FB4, and so on, every block where there is used SFB41.
It has to be something about the SFB's I think, I mean, can my 315-2DP handle SFB41 ?

Here is the project that I uploaded with 'Station Upload':
 
hi,

[from Siemens]
There are two versions of the PID control function, although they are technically identical:
  • FB41 - 43 are part of STEP 7.
  • SFB41 - 43 are integrated into the operating system of certain CPUs ("Technological CPUs").
[/from Siemens]

so, if you want to use the PID-blocks in S7-315, call the
FB- blocks instead of the SFB-blocks.


HTH
Rolf
 
Technological CPU's

Hi,

Well, I want to use the same CPU of the allready installed machine. That is a 314C CPU. But I did a test on a 315-2DP because that was a spare part that I had.

So, u say that in some CPU's SFB41 is integrated, and some not ..

Well, I found something on the internet, seems that CPU 313C and 314C have those blocks.

Why a 315-2DP, a version higher then a 314C I guess doesn't have these blocks ?
 
Combo,

you might think a 315-2DP is higher than a 314, but a 314C is more recent. So it's not a question of the highest CPU, but of the most recent one. I guess if a new 315 is released, it will have the SFBs on board.

Kind regards,
 
2ag10

The 315-2DP 2AG10 version, I thought that this was a recent CPU.

We have 315-2DP's 2AF02's also, and these ones are the old ones.


But I guess that you're right.
 

Similar Topics

When I go PLC - Upload station to PG and select the IP address of the CPU (it finds it), I click OK and get the message "Online: The connection to...
Replies
7
Views
912
I'm working with a Siemens C7-633P (S7-300 integrated with OP7 HMI) and Simatic Manager V5.3, SP3. My problem relates to uploading the software...
Replies
5
Views
6,901
S
I`am trying to upload an S7 program from PLC to PG. The plc is also connected to an industrial PC and touch screen. I`am selecting rack 0 slot 2...
Replies
2
Views
4,459
shamus
S
Hi, I'm trying to export data from a DataGrid to Excel using VBA, but I'm getting an error "Object doesn't support this property or method". The...
Replies
0
Views
61
Hello, I have a CNG compressor that is run by a PLC. I tried to get team viewer on it to be able to view it remotely, I accidently disabled the...
Replies
0
Views
95
Back
Top Bottom