Omron CP1L. CX Programmer. How do I fix so that a CNTRX(548) remembers the count it had before a power failure?

I need to know how many cycles something has happened, even though the main power fails.
 
Why use a counter just increment on a pulse a retentive integer or double if large counts.

Was just hoping it was a quick fix, hehe. Since I am just doing maintenance on a machine here...

Guess I can try what you said.
 
According to the manual counters "CNT" are retentive on power failure, I assume this is only if a battery is fitted See P28 of this manual.
Not used Omron in many years so CNT function may be different than the "C" type, many PLC's now support internal counters as before i.e. "C001" and the IEC function "CNT xxx" so it may be that only the latter is retentive.

http://www.jwtech.co.th/downloadjwtech/omron/omronmanual/CP1H.pdf
 

Similar Topics

Hi everyone! I have an issue with some Omron CP1L-E PLC's. They're connected to get the info from production machines, but I've noticed that...
Replies
2
Views
1,149
Hi! Newbie here... Cx-programmer CP1L PLC NB7 HMI I want to multiply something i by 1,5 in CX-Programmer to get a higher number to use in HMI...
Replies
7
Views
2,215
Hi all, I've been upgrading some machines recently which involves installing a 10" NB HMI, HUB and a CP1L-E to avail of the built-in ethernet...
Replies
0
Views
1,699
Hi, is someone experiment connecting a Omron plc CP1L with a Siemens HMI TP1200?, i've installed the drivers in WinCC , plc options is just CS1 or...
Replies
0
Views
1,906
Hi all, Does anyone know if you can have a CP1L CPU communicate with two NB HMIs via an Ethernet switch. Both HMIs would have different functions...
Replies
2
Views
1,465
Back
Top Bottom