I was modifying some code and saw a strategy for heating and cooling that had me wondering.

BAsically the PID output (0-100.0%) is compared to a cyclic (10 seconds)

So, if the heating is called 20% at the PID control block, the heating will be called for 2 seconds out of 10 seconds. Like wise cooling will be called when the PID goes negative. There is a deadband of maybe +/-3%

Does anyone know the name for this type of control, and why anyone would use this rather than the PLC PID function directly
 
It's called a time proportioning output. Some also call it pulse width modulation, but usually on quicker time cycles.

It is used where your heating or cooling device is an on/off system, not a full modulating system. For instance, we have gas fired furnaces at our shop. The burners are setup to operate at full flow, no modulation. In order to control the heat in the furnace, the PID loop calculates an output that is fed to a 120 second time proportioned digital output. The thermal mass in the furnace keeps the temperature steady. This setup is often used where full modulating control would be more expensive than a simple on/off system and provide little or no benefit.

Edit: Looks like Mickey beat me to the punch.

Brian
 
I use this method for seal bar heating when temperature controllers are not called for in the project. I have had pretty good luck with it.
 
Heat/Cool is also called duplex control. It's used in food, chemical and pharma processing for jacketed vessels - heat supplied by steam or hot water, cooling by chilled water.

Time proportional provides straight line control rather than the inherent saw tooth response of on-off control.

Time proportional is also used extensively for electric heat temp control on things like sealing bars or extruder zone control.

Dan
 

Similar Topics

Just wondering if anyone else does this kinda stuff. See image. I thought it to be appropriate to embed in grouped items. PV5310 with standard...
Replies
3
Views
576
All Performed a managed ROCKWELL download before lunch. When it was finished it opened the file folder of were it loaded too. Customer called and...
Replies
4
Views
1,456
I'm thinking of the MSG as an AOI just because I couldn't think of another example that would have the same prefix with different suffixes.. you...
Replies
4
Views
1,718
i have been assigned a project where the COD levels (Chemical Oxygen Demand)in the effluent is to be monitored. I have done some research on the...
Replies
7
Views
2,355
I just read this article in Control Magazine. It was pretty interesting how what could be a simple mistake can cost $2.5 million US. Luckily no...
Replies
14
Views
5,739
Back
Top Bottom