L33ER major fault

Join Date
Mar 2012
Location
Jakarta
Posts
29
Hi, guys..

So we had a problem with PLC AB L33ER ver 21.11 for compressor control panel.
After running well for 3 months, suddenly there was PLC fault shutdown signal.
When we checked it out, it was major fault code 061 (please see attachment).
So we cleared out the fault, download the program again and it worked again.
But after 24 hours, the same problem occured again.

Do you have any suggestion on this problem?

Thanks n regards,
Kardel

major fault 9600.jpg
 
From this useful manual http://literature.rockwellautomation.com/idc/groups/literature/documents/pm/1756-pm014_-en-p.pdf it says the following for error 61.

Cause
1 61 For a controller with a memory card installed, the controller:
• Detected a non-recoverable fault.
• Wrote diagnostic information to the memory card.
• Cleared the project from memory.

Recovery Method
1. Clear the fault.
2. Download the project.
3. Change to Remote Run or Run mode.
If the fault persists, contact Rockwell Automation support.
 

Similar Topics

Hey guys, On my system, i got prop valve controling cylinder on the left and right to adjust the center of a lumber before it get in a woodmill...
Replies
8
Views
925
Hi Friends, I have an upcoming project were I need 20 pcs of ModBus TCP Clients / AOI. to control 10 devices I use 20 transactions to control 10...
Replies
4
Views
740
We have a machine that has a 1769-L33ER and we were wanting to connect it to our plant network. Currently has a local network for drives and HMI...
Replies
1
Views
847
So, here's the situation the best I can explain it. I have a 1769-L33Er that uses a set of recipes selected by the customer via FT SE on a...
Replies
4
Views
1,650
I'm trying to get an upload from a machine for backup purposes. The upload seems to work fine but at the end I get errors and no upload. It...
Replies
2
Views
1,392
Back
Top Bottom