RS485 Modbus Temp. Controller Issue

Plutonius

Member
Join Date
Nov 2013
Location
Xenia Ohio
Posts
14
I am currently have a bit of an issue connecting to a Love 2600 temperature controller via RS485 full duplex with a Grid Connect NET485 Modbus RTU to TCP ethernet bridge.

I first hooked up the temperature controller to a run of the mill RS485 to USB converter and it worked great. Polling was effortless and easy.

Now when I try to connect to the NET485 module I receive nothing but timeouts. I double checked all my settings and my wiring to no avail.

Lastly, thinking that perhaps I had a faulty gateway, I hooked up the RS485 to USB converter to the NET485 and used a Modbus slave simulator to replicate the temperature controller as my computer. Polling worked great there as well. Talk about frustrating!

The manufacturer of the Ethernet bridge did say their device drives a 3.5V RS485 signal that maybe too weak for the Temperature controller to receive properly. I also have no signal ground as the temperature controller has no spot for it. Has anyone else ran into a issue similar to this one?
 

Similar Topics

I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
6
Views
139
I am trying to figure out some communication specifics for a Modbus RTU network that I will be integrating with and could use some help to make...
Replies
9
Views
2,068
I'm getting no response from a device I'm trying to communicate to with a Beckhoff IPC. I'm not sure why it's not working. Attached are pictures...
Replies
0
Views
615
HI guys: I am attaching several diagram from several sources, it seems to be that there is no such a wiring standard for modbus RS485 RTU. In some...
Replies
24
Views
4,500
So I'm working on an old project I did several years ago. It has 12 nodes on a modbus RTU network. I'm going back for an expansion. I'm going to...
Replies
5
Views
1,882
Back
Top Bottom