CompactLogix L18 Date and Time

dmayhugh

Member
Join Date
Sep 2016
Location
Michigan
Posts
48
I am using GSV for Wall Clock and created a controller tag to get the Date and time values. When power is removed from the processor I loose the current Date and Time. How do I retain the date and time when power is removed?
 
I had to update the firmware version on the 1769-l18 controller. it was 20.14 and I flashed it to 20.19. This resolved the date defaulting back to 1997 when power is cycled.
 