S7-400H Hardware redundancy configuration

naturephoenix

Member
Join Date
Jan 2015
Location
Vienn
Posts
181
Hello all.

This is my hardware equipment:
This is order inside TIA selection tool: (but I'm tryinng to make program inside STEP 7 v5.5 sp4)
1. 6ES7405-0DA02-0AA0 (PS)
2. 6ES7412-5HK06-0AB0 (S7400H CPU)
3. 6ES7405-0DA02-0AA0 (PS)
4. 6ES7412-5HK06-0AB0 (S7400H CPU)
5. 6ES7153-2BA10-0XB0 (ET200M IM 153-2 )
6. 6ES7153-2BA10-0XB0 (ET200M IM 153-2)
7. 6ES7321-1BL00-0AA0 (DI x 32)
8. 6ES7321-1BL00-0AA0 (DI x 32)
9. 6ES7321-1BL00-0AA0 (DI x 32)
10. 6ES7321-1BL00-0AA0 (DI x 32)
11. 6ES7322-1BL00-0AA0 (DO x 32)
12. 6ES7322-1BL00-0AA0 (DO x 32)
13. 6ES7331-1KF02-0AB0 (AI x 8)
14. 6ES7331-1KF02-0AB0 (AI x 8)
15. 6ES7331-1KF02-0AB0 (AI x 8)
16. 6ES7331-1KF02-0AB0 (AI x 8)
17. 6ES7332-5HD01-0AB0 (AO x 4)
18. 6ES7350-1AH03-0AE0 (FM350-1 COUNTER)

This I'm trying to configure inside step 7 v5.5 sp4
I did that on this way inside STATION H, take a look picture 1
I'm able to do compile without problems.
I've noticed following : Modules addresses inside (ET200M IM 153-2 for 1. PLC) and (ET200M IM 153-2 for 2. PLC) can not have same ADDRESS. Take a look picture 2.
If I open each module inside properties I can choose redudancy module, so I choice appropriate
module from different DP Master. Take a look picture 3.
I'm able to do this for DI and DO modules, but for AI, AO and COUNTER nope. Take a look picture 4.
Why is that case, am I doing anything wrong with hardware configuration?

Project is uploaded here as attach, and here are links for pics:
pic1 : http://i.imgur.com/1whdlCq.png
pic2 : http://i.imgur.com/GAxIsI0.png
pic3: http://i.imgur.com/8MLes56.png
pic4 : http://i.imgur.com/32Eb7Zh.png

THX in advance
 
I think atm that my configuration is wrong since I have only 1 set of hardware modules, but inside my configuration I placed these modules inside both of
IM 153-2.

Why I need two IM153-2 is just for 2 profibus connectors.
 
Two IMs

Hi,

You require two IM per ET200M station. One IM is connected (using PROFIBUS) to one CPU and the other IM is connected to the other CPU.

Best regards,
Kelkoon
 
Hi,

You require two IM per ET200M station. One IM is connected (using PROFIBUS) to one CPU and the other IM is connected to the other CPU.

Best regards,
Kelkoon
So I should delete one ET200M from hardware configuration? I AM trying just PLC CPU redundancy not Module redudancy. ET200M comes with 1 or 2 profibus ports? If it is just one than I need second jist to link CPUs?
 
Hi,

You require two IM per ET200M station. One IM is connected (using PROFIBUS) to one CPU and the other IM is connected to the other CPU.

Best regards,
Kelkoon

For just CPU redundancy I think 1 IM 153-2 is required.
It comes with 1 DP port but serial PROFIBUS connection is needed between
2 CPUs and 1 IM 153-2
 

Similar Topics

hello s7-400h and wincc are connected to each other via Ethernet. I need help on how to do time synchronization
Replies
0
Views
34
Hi, I'm setting up comms at a station and I'm working with Cisco IE 3400H switches. I have been able to configure them following the Harware...
Replies
7
Views
581
Hello All, For S7-400H system, can we make this redundant PLC (connected to one uplink switch) to communicate simultaneously with 3rd party HMI...
Replies
2
Views
1,437
Our customer has S7-400H system for turbine control.This system communicated other different systems by CP443-1 card.Plc cycle time 6000ms.SFC108...
Replies
6
Views
1,904
Hello everyone, I am lookimg for some help to figure out where come from the problem or what i can do to improve the latency. PLC: S7 416-5h...
Replies
7
Views
2,984
Back
Top Bottom