So.... where does that leave me? Can I safely connect the A1000 drive to corner-grounded 240V power without letting the smoke out or not? Do I have to remove the MOV filter network in the front end / is that possible?
-rpoet
It's your call, but the only SAFE option in my mind is to install a "drive isolation transformer" ahead of the drive. It would be 230 Delta primary, 230/133V Wye secondary. You don't USE the 133V L-N voltage of course, but it creates what the VFD components are looking for, a solid reference to ground on the input line voltages.

Example only, not an endorsement:

If you were (hopefully) going to use a Line Reactor, you can eliminate that as this transformer will provide the same level of drive protection as the reactor would have.
 
It's your call, but the only SAFE option in my mind is to install a "drive isolation transformer" ahead of the drive. It would be 230 Delta primary, 230/133V Wye secondary. You don't USE the 133V L-N voltage of course, but it creates what the VFD components are looking for, a solid reference to ground on the input line voltages.

Example only, not an endorsement:

If you were (hopefully) going to use a Line Reactor, you can eliminate that as this transformer will provide the same level of drive protection as the reactor would have.

The compressor is a pre-packaged unit, and comes with a line reactor installed.

I got written confirmation from Yaskawa that the drive would be OK on corner-grounded delta power, for whatever that's worth. They also said I should install "ground fault protection" on the circuit supplying the drive, and when I pressed the tech he couldn't really explain why or how that would help; it seemed like a CYA to me, and goes to your point regarding Yaskawa not really understanding delta power.

Anyway, the drive powered up without any issues, and is running without a transformer. Time will tell if issues crop up.

Ugh. I hate corner-grounded delta power.



-rpoet
 

Similar Topics

Hi, I want to do an electronic line Shaft with Yaskawa A1000. I think a must update firmware. Do is a user that have a firmware for this? I...
Replies
0
Views
770
Hello friends, I have Yaskawa A1000 drive and I want to activate a safety function during starting a drive .🤾 I have assign frequency...
Replies
4
Views
1,728
Im assisting a customer with a Yaskawa A1000 drive. The machine came from China The part number is CIMR-AB4A0023FBA Can someone help me find the...
Replies
9
Views
2,510
I’m working on an application where I would like to mount the encoder on the end of the gearbox instead of the motor Can I hear from any of the...
Replies
2
Views
1,874
Has anyone ever tried to connect an HMI to a Yaskawa A1000 VFD? If so, what HMI did you use and what communications protocol? I want to try to...
Replies
4
Views
2,062
Back
Top Bottom