Dear all,
i have a project that contains an encoder and i use speed counter from siemens to count from the encoder.
i'm using a linear magnetic encoder to measure the displacment of press machine and i connect the encoder with the speed counter but i don't know how to program the speed counter to show me the displacment of the press machine on HMI.
 
First do the engineering.

Do you have one of these?
http://www.mtssensors.com/technology/how-magnetostriction-works/index.html
or something like it?

If so then you are going about this wrong. You should probably get a rod that outputs an analog signal. The reason why what PLC people call a high speed counter is a joke and they don't count fast enough to provide accurate position so it is best to have an analog output that provides you with an analog signal proportional to the position.

The speed of the pulse is about 2800 m/s. A typical high speed counter card can count 20Khz so 2800/20000=0.14 meter resolution which isn't very good. One can do better with proximity switches.

A second option is to buy a card that is designed to interface with the MDT rods ( magnetostrictive displacement transducer ). A normal "high" speed encoder card will not do.

A third option is to buy a controller that is designed to control presses. The can also control position or force or limit both. I am assuming you have an hydraulic press. These controllers have counters that count as high as 240 MHz which will result in just 0.1666E-5 resolution. About 17 microns. Better yet is to use MTDs with SSI interfaces. The the resolution can be as fine as 1 micron.
 

Similar Topics

Hello Folks, Has anyone configured a Momentum high speed counter on Unity 13.1. We need the wiring diagram for Momentum High speed counter and...
Replies
0
Views
76
i am bench testing a 1734 -VHSC24 Point I/O High Speed counter module, i cannot find any examples of wiring the outputs from the module. does...
Replies
4
Views
1,378
Hello guys, I have created a program where I count the high speed inputs of a flowmeter and create pulses per second to check the flowrate. Next I...
Replies
5
Views
1,784
Hello to all, I don't have to much experience in the PLC. I'm using the Studio 5000 v32.03 We are trying to measure the length of a product, in...
Replies
3
Views
1,119
Does anyone know how to set the output window on-off values on the fly without having to inhibit the module? I could of sworn when I first started...
Replies
11
Views
2,376
Back
Top Bottom