analog input simulator

plc noob

Member
Join Date
Oct 2007
Location
atlanta , georgia
Posts
258
guy's

i am trying to learn / teach myself analog i/o . and i need a way to simulate an analog input .i have been told that you can wire the analog output to the analog input . will this damage anything on most cards ? right now i just have a 0-10 volt analog in card . i have seen peanple make simulators from potentiometers . but i need to know the size / value and how it is wired . did not seen to find anything on the net ? can anyone help ?

thanks in advance

noob
 
Noob,

If your Analog Out has the same range (4-20 miliamp, or 0-10 VDC) then it would not do any damage to wire the output to the input.

What Input card do you have, and what brand and model of PLC?
 
Let's assume you have a 24 VDC supply available. Get a 10K pot and a 15 K resistor. Connect the 15K resistor to one leg of the pot. Connect the other side of the 15K resistor to DC+. Connect the other leg of the pot to DC-. Between the wiper of the pot and DC- you will be able to read from 0 to almost 10 volts. How close to 10 volts depends on the actual resistance of the pot and the resistor, and the actual voltage output of the DC supply.

The current across the resistor/pot combination will be 24 volts/25000 ohms, or approximately 1 milliamp. That's 0.025 watts. Just about any resistor and pot you're likely to locate will be able to handle that.

Consult the wiring diagram for the analog input module you're using to determine how to make the connection to your PLC.
 

Similar Topics

Howdy! I'm a PLC newbie and would like to know if there is a PLC simulator with Analog Input\Output emulation Thanx in advance
Replies
2
Views
4,949
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
17
Views
314
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
8
Views
187
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
Replies
1
Views
80
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
58
Back
Top Bottom