how to take the data from level transmitter to analog input omron?

kartika

Member
Join Date
Jul 2011
Location
Lampung
Posts
31
hi all...i'm still confusing about scaling in PLC..need ur help, please..
i have a differential level transmitter, the signal is 4-20mA,and analog input Omron CS1W-AD161-V1 (16input channel), how can i take the data from the level transmitter to the analog input?
thanks for the attention
 
thanks for jvdcande, but would u like to explain more to me, because i'm still confusing about it...
i read that it just MOV the data from sensor and then transfer it to memory, is my opinion right? do i need another instruction or just MOV and transfer it?and how can i set the data that say 4mA is 0% and 20mA is 100%...?
best regrads..
 
The raw data will be the allocated input channel.
You will need to review the W345 manual. It will explain where the data will be based on the Unit Number of the module that is set on the two rotary switches on the front.
You can scale the raw value with the SCL instruction.
This instruction is explained in the W340 manual.

Hope this will help.
 

Similar Topics

hi all...i'm still confusing about scaling in PLC..need ur help, please.. i have a differential level transmitter, the signal is 4-20mA,and...
Replies
0
Views
3,113
Hi guys I have Productivity Station which will collect Run time data from Phoenix input block "ILB ETH 24 DI16 DIO16-2TX". I am new to crimson...
Replies
0
Views
2,901
Hi folks, I'm not as accustom with Siemens & WinCC, however I've been asked to increase the amount of data an existing application is logging...
Replies
2
Views
52
Has anyone migrated Proficy Historian data to a new server? I followed the guide to move all the data over, but when I run the utility, it stops...
Replies
0
Views
43
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
246
Back
Top Bottom