Hi!
I want programming a new AB with 1756-L55 controller & 1756-M13 memory board, but the RS232 lit solid red and the OK too. Why ? :(
Thanks!
Pedrosz
 
Did you upgrade the firmware of the controller, as this is required
before downloading your program? The firmware is available from Rockwell.
 
hi

these two leds lit together indicate that the controller is in a i be dead scenario. The controller has encountered a major fault and shutdown, clearing it's memory for good luck as well. Thing to check
assuming that you have already flashed the controller to start withare

the revision level of the firmware, one revision of 11, can't remember which will produce this problem if the power is cycled rapidly to the rack.

Have you any message instructions running, if so don't pull the connection out, e.g. dh+ or ethernet cable. This was fixed by revving the firmware also.

Too many messages down the rs232 port....if you can solve this let me know, as this is driving us crazy. It will fault and shut the plant down.
 
No guessing or searching required

OK, it's brand new, right ? And the OK and RS232 LEDs are both solid red ?

The CPU has no firmware installed. They all ship that way.

RSLogix 5000 has a Firmware Download feature that starts ControlFlash, or you can start ControlFlash from the Start menu in Windows.
 
Ok ,but for the firmware upgrade I need to be in online with the PLC (the ControlFlash dosn't activ in RSLogix5000/Tools),and I think that isn't possible while the RS232 is red. ???
 
The firmware upgrade running.
1.The ControlFlash was inactiv because wasn't installed
2.The RS232 was solid red because the processor unit has two krooked pins.(pins ok -> Ok flashing &RS232 off -> ok)
 
I stand corrected, pedro and kevin. You're right about the flashing red LED being standard no-firmware mode, and the solid red LED indicating a hardware failure.

Good work troubleshooting the crooked pins. Did the controller accept firmware once you straightened them out ?
 

Similar Topics

i have an device which can support serial (RS485,RS232),CAN protocol . i want to connect it to an existing MIB 1553B bus ,what device will I need...
Replies
0
Views
57
Hello: I have to connect a RS232 Modbus RTU slave that only has Tx, Rx and GND signals to a Modbus RTU master. However, all RS232 to RS485...
Replies
3
Views
204
Hi to everybody. I need to read the first 12 characters of the message that a barcode reader sends to the ascii card (1734-rs232 ascii) and I...
Replies
8
Views
686
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,479
I'm trying to manually convert a Beijer E200 HMI project onto to a new Mitsubishi GOT gs2107-wtbd. The PLC is a very old A-series AS1CPU and is...
Replies
1
Views
364
Back
Top Bottom