Hi,
I am trying to do a very simple program to communicate the PLC with Hyperterminal.
I am using a new CP1W-CIF01 Optional Board (RS232) with an almost new PLC CJ2M-CPU31. But something is not working.
About the wire, I have checked it several times and I think it should be OK. I am using a USB-RS232 CH340 (pinout attached). Its driver is working, I have already used it, and windows is detectig it properly. I have tried it with an intermediary wire following the manual (also attached). Tired of no solutions, I have also tried it without this intermediary wire given I remember I used directly the USB-RS232 with other OMRON and that worked.
Anyway, I only connected the optional board, but I did not make any additional setup to let the PLC knows that this board is already connected. I was looking in the manuals W472 and W473 about if it is necessary to include it in the I/O Table Setup or other additional setup, and I would say it is not necessary. So, I only connected the Board and I modified the Settings of the Serial Communications (attached).
When I try the "Direct Online", Cx-Programmer starts the scan for the right serial configuration, the COMM led starts blinking in the board, but the scan ends with a "Failed to connect" message.
So, finally, I connected to PLC via Ethernet and I uploaded the program. The program is very simple (attached). However, A392.05 and A392.06 are allways OFF, even if I force the Reset A526.00. Why??!!
A particular issue, that may could help you to detect the problem, is that when I force a bypass for A392.06 (W232.01), I got an Error in the Error Log (0x02F0 "Non-fatal Inner Board Error").
Thank you very much.
I am trying to do a very simple program to communicate the PLC with Hyperterminal.
I am using a new CP1W-CIF01 Optional Board (RS232) with an almost new PLC CJ2M-CPU31. But something is not working.
About the wire, I have checked it several times and I think it should be OK. I am using a USB-RS232 CH340 (pinout attached). Its driver is working, I have already used it, and windows is detectig it properly. I have tried it with an intermediary wire following the manual (also attached). Tired of no solutions, I have also tried it without this intermediary wire given I remember I used directly the USB-RS232 with other OMRON and that worked.
Anyway, I only connected the optional board, but I did not make any additional setup to let the PLC knows that this board is already connected. I was looking in the manuals W472 and W473 about if it is necessary to include it in the I/O Table Setup or other additional setup, and I would say it is not necessary. So, I only connected the Board and I modified the Settings of the Serial Communications (attached).
When I try the "Direct Online", Cx-Programmer starts the scan for the right serial configuration, the COMM led starts blinking in the board, but the scan ends with a "Failed to connect" message.
So, finally, I connected to PLC via Ethernet and I uploaded the program. The program is very simple (attached). However, A392.05 and A392.06 are allways OFF, even if I force the Reset A526.00. Why??!!
A particular issue, that may could help you to detect the problem, is that when I force a bypass for A392.06 (W232.01), I got an Error in the Error Log (0x02F0 "Non-fatal Inner Board Error").
Thank you very much.