Have to upload every time when going online with SLC 5/04

mjggjm12

Member
Join Date
Jul 2013
Location
NH
Posts
92
For some reason every time I go online with one of our SLC 5/04s It makes me upload the program even though the only differences between the offline and online program is some tag values. I have had this problem before with PLC 5 in the past, but can't remember why. I should mention that this started happening after a program modification. Thanks everyone.
 
When I upload a program I often get this, so I automatically download the upload and save it, then go online with the new save.

For some reason the checksum gets off, and this especially happens if it is a SLC5/05 and the upload changed the IP address or settings.
 