InTouch, Unity, addresses dont match

Milestogo

Member
Join Date
Aug 2019
Location
Montreal
Posts
19
Hello,

I'm running my Plc in PLC Simulator (Unity Pro XL).

Intouch sees the connected links but the tags are not matching
(+1 on InTouch).. o_O

example :
Intouch : %MW1950 Equals %MW1950 on the PLC datas.

I've been told it has something to do with the NodType.
It was set to Modbus by default, since most of our other plcs on the network are configured that way. This one PLC is Tsx premium..

Is there a way to adjust the starting address, either on Unity or SMC perhaps?

Thank you for your hindsights!
 
Generaly Modbus drivers have in configuration option to select if addressing is normal or +1. As I record InTouch has it, but I didn't use it for quite awhile.
 
Hello,

I'm running my Plc in PLC Simulator (Unity Pro XL).

Intouch sees the connected links but the tags are not matching
(+1 on InTouch).. o_O

example :
Intouch : %MW1950 Equals %MW1950 on the PLC datas.

I've been told it has something to do with the NodType.
It was set to Modbus by default, since most of our other plcs on the network are configured that way. This one PLC is Tsx premium..

Is there a way to adjust the starting address, either on Unity or SMC perhaps?

Thank you for your hindsights!

This is normal, it's just that the PLC will be 0 based, the driver in InTouch 1 based so need to add an offset, in most SCADA applications you can change this with driver settings if required.
 

Similar Topics

Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
5
Views
110
Trying to export a Modern application for an upgrade to Intouch 2020 but I cannot export the application from the 2014 version because the export...
Replies
2
Views
103
Hi guys, I have experience with PLC to Excel etc...just starting on using intouch scada screens. I have an Excel sheet that uses mainly...
Replies
1
Views
139
Currently we have a fat( I think that is what it is called) Intouch application. An application resolution of 3840x1080, and inside that 2x...
Replies
0
Views
90
Hi guys We're in the process of creating a ME runtime to operate on a PC running windows using a InTouch INDT156 touchscreen, and we're having an...
Replies
3
Views
140
Back
Top Bottom