Wire (24 VDC)

kirk

Lifetime Supporting Member
Join Date
Jul 2003
Location
Houston
Posts
71
Ok, so what are the standards?

For years I used Blue for all my 24 volt DC, 16. or 14. It seems a bit big, and can be hard to make look ..... clean.

I know another panel builder and he uses Red and Black.
It makes sense in a way, you hand anyone on the planet a pair of Jumper cables, and they know the Red is + and Black is -. I see the logic for DC

The problem becomes in AC voltage black is Positive

But then you have cable(Belden 18-4, for instance) where Blue isn't even an option.

Then I came across some Black and red paired "Primary OFC" comes in the gauges I need for inside a panel, but It looks like it may be speaker wire. Well, that isn't very professional, so I am guessing that is out, right? Or no?

what are the rules?

IMG_1262.jpg IMG_1261.jpg IMG_1263.jpg IMG_1264.jpg
 
IEC state dark blue positive and negative. However I use white as negative. To use one color for both positive and negative isnt really good in my opinion .

Wire thickness is relative to your fuseing
 
For 24VDC I always use solid blue for + wht/blu for -. In panels where I have had a handfull of low voltages. I have used blk/red for 12V+ red/blk for 12V-. Pretty sure NEC only specifies two colors if I remember correctly, Orange and Green. Orange for where line voltage is still present, green for grounds. Sure I will get corrected if wrong.


Edit: Well think I was wrong on NEC for orange NEC article 110.15 says for the high leg, maybe I got the Orange for line voltage still present from NFPA.

looks like a nice collection of info: https://www.electricaltechnology.org/2020/07/electrical-wiring-color-codes-nec-iec.html
 
Last edited:
NFPA 79 is the "electrical standard for industrial machinery". whether your equipment falls into this standard is up to you to determine. If so, the wire colors that are "standard" are outlined for you in chapter 13. NFPA 79 is available for free online viewing if you register an account.
 
Ok, so what are the standards?

The problem becomes in AC voltage black is Positive

There is no such thing as AC positive. There is AC phase and AC neutral. According to IEC DC conductors are dark blue, but it is allowed for DC- to have stripe.
AC phases are black.
AC neutral is light blue.
If we have AC from isolated transformer which is used in control circuits then the colors for both conductors is red, but it is allowed for neutral to have stripe.
When it is question about interconnection then it is orange.

Ground is always green/yellow.

All previous is regarding to conductors that are not in cable, when there is cable there are different set of rules.
 
As far as I know there is no code standard for 24V systems but what I use and I find it works fairly well is
24- from the supply Blue with White stripe
25+ from the supply Blue with Black stripe
controls wires just Blue
safety circuits connected to safety monitor relay Blue with a Red stripe
all are normally 18ga unless their is reason to increase it
the this color pattern makes it easy to identify them later nd keeps the DC nut separate from the 120vac Nut
 
I used light blue for the neutral, which is the same for AC and DC, all the neutral cables for AC and all the 0V cables for DC come from a unique insulated bare copper bar connected in a single point to the main ground, located on the main cabinet near the connection terminals and that saves many terminals.

The neutral and 0V cables from outside go direct to the neutral bus bar without going through terminals.

For AC phase cables black color, for + 24VDC dark blue
 
DC Volt = Dark Blue = brown (European)
DC com = White/blue strip = dark blue (European)
AC volt = Red
AC neutral = white
3 phase volt = red/yellow/brown = black
interlock wiring between panels = orange
ground = green = green/yellow strip
 
In my plant the electrician uses whatever color wire is laying around in the back of the van. Makes it hard to figure stuff out sometimes.

When I design a panel it's
24+ Blue
24 common blu/wht

120VAC unswitched black
120VAC control red
120VAC grounded conductor white
 
Every plant I have been in that has a standard (and ours) is:
Black: 120vac hot for circuits like lights, plugs AC powered devices in the panel, power to an AC output card.
White: AC neutral only.
Red: AC control wiring input and output.
Green (or EU green/yellow): Ground only. Never ever potential of any kind.
Blue: +24vdc
Blue/white (and sometimes white/blue): 0vdc. Even if 0vdc tied to ground or neutral.
Yellow: External wiring that could have any external potential on it.


Those are the major ones. Other vary from plant to plant.
 
I use Brown for my DC+, White/Blue DC- and Blue for all my DC inputs/outputs
 

Similar Topics

Quick question: Can I run 24VDC signal wire (shielded) in the same 1 inch conduit with 2 cables (+ & -) with 90VDC to power a permanent magnet DC...
Replies
13
Views
2,734
HI All, I have a cooler fan 24VDC. This has a fly lead with 7 cores. Black, Blue, Brown, White, Green, Yellow, Yellow/Green I have contacted...
Replies
4
Views
1,903
I have to build a industrial control panel for Austrailia that has a 24VDC Allen Bradley power supply for use in the PLC, what are the correct...
Replies
10
Views
5,447
Hi there, i was hoping for some oppinions from you all with regards to colours on +24VDC and -0VDC wires should be? To me the most common...
Replies
29
Views
19,775
I want to energize a relay with 24VDC on CAT5e cable over approx. 130ft from a PLC. My concern, before actually running the cable, is that the VDC...
Replies
11
Views
12,102
Back