good afternoon everyone, I was researching about the tcp / ip connection
with cp 443-1 and iba and found that the cpus that are communicating data
Correctly in iba and that communication is ok (imagen_00) is because in the
in cp 443-1, the initial state sending and
receiving correctly (image_01) and the cpus that the iba does not recognize
in cp 443-1 they are not configured and mark me in cp send / recv communication
stop mode (image_02) my question is how to do the configuration and the link
Someone can guide me how to make the configuration and the link from the netpro of simatic manager.

IMG_00.jpg IMG_01.jpg IMG_02.jpg
 
You are configuring an OPC connection to an S7-400 via a CP443-1.
Is the IBA software the OPC server or the OPC client ?

How is the OPC connection setup in the OPC Server ?
 
In the OPC Client, what is the name of the OPC Server it connects to ?


Jesper, maybe I don't understand you but the connection you make is not op server, it is tcp as indicated in image 03.
Now how can it be that the first three connections with tcp are established and the fourth is not, why is this happening?

IMG_03.jpg
 
OK, it is not OPC.

I guess the IBA software is able to establish a TCP connection directly.
Did you setup the previous 4 TCP connections ?
I also think that the previous 4 connections are socalled unspecified connections (ID del interlocutor is empty).
Adding one more unspecified connection in the same way should be possible. A problem may be if the CPU or the CP has run out of connection resources. Investigate the Connection tab of the CPU properties. There should be listed how many connections are in use, and how many are free.
 
It appears that you have started another thread about the same topic.
In that thread, Petrozawodsky posted this:
Can not understand your question.
iba TCP/IP S7 works as one-side connection: PLC cyclically send packets to PC.
All needing configuration was prepared in PLC program.
IBA only listening and receiving messages from PLC.
To get more detailed information - goto iba-ag.com , make registration and download apropriate manual.
So it seems that IBA requires that the PLC sends data, which probably require that a connection is setup on the PLC side.
The best is to exactly follow the instruction in IBAs documentation.
 

Similar Topics

Dear All We have 4 PLC for different PLC's which uses 443−1EX20−0XE0 in the physical hardware but configured as 443-1EX11-0XE0 in the Hardware...
Replies
10
Views
2,926
I have a S7400 414-2 DP fw5.3 with a CP443 6GK443-1EX30 fw3.0 and FM350-2 on profinet The interface module is a 6ES7153-4BA00 fw 4.0 (ET200M...
Replies
7
Views
1,907
I am troubleshooting the setup of UDP broadcast receiving on a CP443-1 CP card. The telegrams appear in WireShark with IP 192.168.1.255 Port 7551...
Replies
6
Views
2,283
Hellow, I'm facing a weird problem with time sync since we've changed from summertime to wintertime. So now it's 12:38 pm in Belgium and the CPU...
Replies
1
Views
1,875
2 CPU's Fiber connected on same rack etc out to a number of ET200s. Set up and running, happily falls over to the other PLC if one switched or th...
Replies
2
Views
1,331
Back
Top Bottom