Question Working with CIP MSG RSLogix 5000

I am trying to send an CIP MSG from a RSlogix 5000 to a 485/ethernetIp device.

I have connected and got a response back giving me the vendor number and such from the device to compactlogix.

I am trying to "Set attribute Single" but I need to send a Data to the device in the following:0x03 0xF5 0x01 0x03 0x00

I did set the CIP Generic Msg with its service code, class, instance, and attribute.

Guess my question is, how do I set up the Source Element to send that Data string?


Any help would be greatly appreciated.
  Reply With Quote
Old July 19th, 2018, 08:57 AM   #2
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 3,643
I've never had to do this but I think it will work.

Create a tag that is a SINT array five elements long. Use the [0] index of the tag as the Source Element and use 5 as the Source Length. Populate the SINT array with the data you listed and, theoretically, you should be good.

Keith
  Reply With Quote
Old July 19th, 2018, 12:24 PM   #3
bnelson14
Member
United States

bnelson14 is offline
 
bnelson14's Avatar
 
Join Date: Jul 2018
Location: Florida
Posts: 3
I tried your idea, but when it runs I get an error. I did use RSNetWorx and set everything up in the Class Instance Editor. I came across and error code on there. [0x0402] Resource unavailable.
  Reply With Quote
Old July 19th, 2018, 12:56 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,011
Welcome to the PLCTalk forum community !

That sounds exactly like a Modbus Mapping entry in a GridConnect Net485 device.

When you request a mapping entry like that, the device tries to verify that it's valid on the Modbus side. If you don't have your device set up correctly on the Modbus side, you'll get an error reply on the CIP side.

Those devices are inexpensive in part because they're so tricky to set up ! Not impossible, but they require both expertise in CIP messaging and in Modbus.

Your next steps will be to capture that error code and carefully examine and test the Modbus side of the device to be sure the Map Entry refers to an accessible Modbus address.
  Reply With Quote
Old July 19th, 2018, 01:38 PM   #5
bnelson14
Member
United States

bnelson14 is offline
 
bnelson14's Avatar
 
Join Date: Jul 2018
Location: Florida
Posts: 3
you are correct it is a Grid connect Net485 device. I was able to use RSNetWorx to set baud rate, data bit, but every time I try to set the input/output mapping I get resource unavailable. Set by step I am getting further.
  Reply With Quote
Old July 19th, 2018, 02:42 PM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,011
When I worked with the GridConnect, I connected the RS485 side to an RS485/USB interface and ran ModSim32 on my PC.

That way I could configure and see the Modbus packets on the serial side, while experimenting with the configuration of the Map Entries.

Once you get one of those devices set up, it's easy to configure more by using TFTP to send the configuration text file to it.

But the initial configuration takes a lot of expertise. In low volumes, it's pretty easy to justify the higher cost of some of the more expensive options (Digi One IA, RTA, HMS Communicator, etc).
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
adding slc 500 to rs5000 for messaging Rippey574 LIVE PLC Questions And Answers 15 September 12th, 2017 05:24 AM
How to access other ASIC registers in Rslogix 5000? csjokerd1123 LIVE PLC Questions And Answers 0 August 18th, 2017 01:48 AM
Studio 5000 Logix Emulate - Is this a free software with RS Logix 5000 or support ? Baker in Virginia LIVE PLC Questions And Answers 33 June 8th, 2017 01:58 PM
RS LOGIX 5000 emulate Skiroy LIVE PLC Questions And Answers 14 August 25th, 2015 04:31 AM
RSLogix Emulate 5000 Restore Image not working PAPO LIVE PLC Questions And Answers 0 April 29th, 2014 10:35 AM


All times are GMT -5. The time now is 01:42 AM.


.