MIGRATING PROJECT FROM PANELBUILDER32 TO FT ME v9

Yes, that's the first step.
Next step is to look at the tag in PanelBuilder and see how it was setup: Ex. exactly which bits was it looking at? How many bits?

Just like Gary said before, take at look at this post for more detail on changing the bit arrays
http://www.plctalk.net/qanda/showthread.php?t=93915
Please confirm this for me:
In PanelBulder32 this Tag 'Ka962a' has the following set up in Tag Editor:
Data Type=Bit Array, Array Size=2, Address=N10:56/2, Description= State extract, Node Name=SLC_1,
On the object representing this Tag on the Display, it has states 0, 1, 2, 3, (ie. number of states is 4)
what precise setting should do in Factory talk for this Tag in order to correct error of BIT ARRAY NOT SUPPORTED?
 
Please confirm this for me:
In PanelBulder32 this Tag 'Ka962a' has the following set up in Tag Editor:
Data Type=Bit Array, Array Size=2, Address=N10:56/2, Description= State extract, Node Name=SLC_1,
On the object representing this Tag on the Display, it has states 0, 1, 2, 3, (ie. number of states is 4)
what precise setting should do in Factory talk for this Tag in order to correct error of BIT ARRAY NOT SUPPORTED?

We can help guide you in the right direction, but you have to take it from there.
That XML file is an import file for graphics. Take a look at the help.
 

Similar Topics

Dear All Recently I prepared one programme in RSVIEW 32 and it is working well, but the customer wants that programme in FACTORY TALK VIEW...
Replies
0
Views
3,309
We are upgrading our FTV ME v8.1 program to SE v12. Is there any way to migrate the alarm tags (about 600ish) from ME to SE. The import / export...
Replies
2
Views
822
Can it easily be done ? We have a legacy project written on Allen Bradly 1746-l542 with Several racks of some on an extension rack and some on A...
Replies
3
Views
1,722
I just want to get others thoughts on what is the biggest obstacle one faces in migrating to a newer system? For me with the few systems I have...
Replies
17
Views
4,077
Hi all, I'm working on migrating some old Sinamics S120 drive units currently integrated in Step 7 5.6/WinCC Flexible 2008 RT to TIA Portal V14...
Replies
7
Views
3,287
Back
Top Bottom