PanelView Screen directed by PLC

rmb550

Member
Join Date
Nov 2009
Location
Ontario
Posts
86
I have been using PanelView T6 and T10 -- and want to use the 3" version in a lower cost application. I am wondering how one gets the HMI to jump to a certain screen based on some status in the PLC --- i.e. if I have an alarm in the PLC (defined by my program) I want the HMI to navigate to a specific screen where the alarms are listed. Note this is as defined by my program in the PLC and is not the "alarms" that are HMI - tag defined.
Thanks in advance.
RMB
 
If you are talking about stanadard Panelviews. Then see picture below.
Pay special attention to the last sentence, you must release control so a operator can change screens again.

ScreenControl.jpg
 
Mickey,
Thanks for that -- but I am using the PanelView Component Operator Interface that has the built in design software, and does not use the PanelBuilder software. Any ideas?
RMB
 
I have not used this functionality with the PanelView Component, but I believe you should be able to control the HMI screen through a PLC tag if you go to: Tags / Global Connections / 19 - Current Screen Number (Read/Write). See attached screenshot.

You can also download the emulator software from Rockwell's site. This will allow you to edit a Component application without having a PanelView Component terminal.

http://www.ab.com/eoi/graphicterminals/downloads.html

PanelView Component Screen Number.jpg
 

Similar Topics

I'm working on a system with three Panelview 7's connected in a DLR. The system started having miscellaneous DLR faults and they were supposedly...
Replies
1
Views
486
I'm doing my first PanelView 5000 application with Logix View Designer v8, and am of course jumping in headfirst. One thing I don't find is a way...
Replies
4
Views
693
Howdy Everyone, We had to replace a panelview 600 2711-B6c20 the other day and when we did, the new one none of the screen selector buttons work...
Replies
5
Views
1,117
I have 2 PV Plus 7 screens used in the same system that both have touch screens that can be challenging to activate after they haven't been...
Replies
0
Views
565
Every time I power this unit up it loses its IP address and goes to DHCP . When I goto the config the IP address is 0.0.0.0
Replies
1
Views
732
Back
Top Bottom