Communicate AB plc with Siemens PLC???

sundar_scada

Member
Join Date
Jan 2008
Location
kumbakonam
Posts
25
Hi to all

I am new for AB plc. Now i want to communicate AB(1756-L61 Control logix) with Siemens S7-300(CPU 315-2DP). I want to transfer all the Tag values from AB to Siemens. How can i communicate the Both.


Thanks in Advance


Regards,

L.V.Sundar
 
The easiest is to add a Profibus interface module in the CLX rack.
Set the CLX module up as a DP slave for the 315-2DP as DP master. In this way you get the most direct connection between the two PLCs.

I know of two Profibus modules for CLX:
SST-PFB-CLX from woodhead.
MVI56-PDPS from Prosoft.
(I wouldnt be surprised if they are actually the same)
 
Hi there,

You can also use a gateway, I believe it will be cheaper and faster to setup. The gateway needs to have Profibus slave interface on one side and slave interface towards the CLX (EtherNet/IP, controlNet, DeviceNet) on the other.
With the gateway solution you will need a minimum of programming of the PLC´s. Set up the gateway as a Profibus slave towards the S7 and set up the gateway as slave on the network used by the CLX.
There are several vendors out there, I work for one of them (HMS).
If interrested, go to:
http://www.anybus.com/support/support-abs-x.asp?ProdType=Anybus X-gateway&Net1=Profibus Slave
and select the network used by the CLX.

BR

Patrick L
 

Similar Topics

hi all i have s5 licened software installed in a latest laptop with window xp operating system. this laptop does not have a serial port.how to...
Replies
5
Views
4,710
Hi everyone, I'm trying to communicate a MultiPanel MP277 touch screen (from Siemens) with a Modicon PLC (984), so, I built the proyect on WinCC...
Replies
5
Views
5,354
I search a dll to communicate my PC to a S7 PLC Siemens. thanks
Replies
3
Views
6,701
Hello i have a PV+1000 firmware ver 5.10 and a compact logix L18ERM VER 24. I googled and read many posts but still can not make simple button on...
Replies
1
Views
553
Have matched communication parameters of both, DOPSOFT HMI and PLC Fatek. Yet an error keeps appearing "Failed to open port COM1". I believe...
Replies
0
Views
674
Back
Top Bottom