We are currently using thermowells to monitor the temperature of water in one of our projects. Its transmitter has temperature range of 0-150 degree celsius and current output of 4-20 ma.
I am currently testing the transmitter by connecting it to my PLC.I am aware of the logic of raw values and measured values in PLC. I know that 4 ma is representing Zero degree celsius & O in PLC and 20 ma represents 150 degrees & 65536 in PLC.
But what I want to know is How much does 4.1 or say 5.1 ma represent in integer form in the PLC in such a case because I cant get a hold on How to interpret the integer forms in temperature units. Any help would be appreciated.
I am currently testing the transmitter by connecting it to my PLC.I am aware of the logic of raw values and measured values in PLC. I know that 4 ma is representing Zero degree celsius & O in PLC and 20 ma represents 150 degrees & 65536 in PLC.
But what I want to know is How much does 4.1 or say 5.1 ma represent in integer form in the PLC in such a case because I cant get a hold on How to interpret the integer forms in temperature units. Any help would be appreciated.