1794-AENT/b

I need to set IP on 1794-AENT/b to 192.168.0.51

I can see 1794-AENT/b from RsLinx when I change a ip to 192.168.1.xxx,(with thumbwheel), and set my notebook to 192.168.1.1

When I tried to change RsLinx goes to Error(Communication fault occur), when I set thumbwheels more than 256, I can't see it from rslinx.

What I should do?
  Reply With Quote
Old March 18th, 2011, 11:31 AM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,426
The thumbwheel is a special setting method on the 1794-AENT and 1734-AENT.

When you set the thumbwheel to any value between 1 and 254, the module uses the common Class C private subnet "192.168.1.xxx", with a 24-bit Subnet Mask of 255.255.255.0. This is the only network number that the module will use when the thumbwheel is set between 1 and 254, and you will get an "object state error" if you attempt to change the address to anything else.

To set the module to another network number (192.168.0.xxx" you must use the BOOTP mechanism and a BOOTP/DHCP Server like the utility that is included with RSLinx Classic. Set the thumbwheel for "999" to make the module use BOOTP.

Set up your PC for 192.168.0.xxx, configure the BOOTP/DHCP Server Utility with network parameters you want (usually subnet mask 255.255.255.0 and default gateway 192.168.0.1) and power cycle the 1794-AENT.

Once you have used the BOOTP/DHCP Server Utility to send the module an IP address, you have to disable BOOTP and DHCP either using the Utility or using RSLinx Classic.

The EtherNet/IP Modules in RSLogix 5000 Control Systems user manual has a very good description of how the thumbwheel-equipped adapters (1734-AENT and 1794-AENT/B, so far) work. It's a very useful manual when you're setting up EtherNet/IP networks. Download it (Publication ENET-UM001) from the literature.rockwellautomation.com website.

Last edited by Ken Roach; March 18th, 2011 at 11:36 AM.
  Reply With Quote
Old March 19th, 2011, 01:54 PM   #3
OleksandrKurdydyk
Member
United States

OleksandrKurdydyk is offline
 
Join Date: Oct 2010
Location: Chicago
Posts: 19
Thank you, I got it to work
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1794 Flex I/O separate power supply russrmartin LIVE PLC Questions And Answers 1 September 2nd, 2009 12:46 AM
1794 AENt communication without controller sebastianswami LIVE PLC Questions And Answers 0 August 11th, 2009 05:40 AM
1794 Flex I/O Error: Mod Config Reject Mfleming LIVE PLC Questions And Answers 4 June 2nd, 2009 07:58 AM
1794 - Ib16 A Joel Mancilla LIVE PLC Questions And Answers 1 October 9th, 2008 09:37 AM
1747sn to 1794 flexio 32bit config problems MicB LIVE PLC Questions And Answers 1 September 23rd, 2005 07:47 AM


All times are GMT -5. The time now is 04:37 AM.


.