Panel view connectivity

krunalc

Guest
K
I have got one Panelview and micrologix plc. Now Panelview has got DH485 port in it. I want to connect my micrologix PLCs with other plcs and would like to put this PLC on ethernet network. For that i know i need 1761 Net ENI module. But in that case how i can communicate PLC with panelview having dh485 port. Is it possible that i put one Net AIC in between so that on PMO2 cable will run from micrologix PLC to Net AIC and panel view will communicate through DH485 port of NET AIC. While connecting HMO2 cable will run from NET AIC to ENI module to connect PLC with ENI module. Does such kind of arrangement will work?? If yes then is there any limitation for such kind of network. I hope my query is clear to u ppl.

regards and anticipating quick responses,
 
I have got one Panelview and micrologix plc. Now Panelview has got DH485 port in it. I want to connect my micrologix PLCs with other plcs and would like to put this PLC on ethernet network. For that i know i need 1761 Net ENI module.

I don't think so - For DH485 comms you will require a 1761 NET AIC module, the ENI module is for ethernet comms.

But in that case how i can communicate PLC with panelview having dh485 port. Is it possible that i put one Net AIC in between so that on PMO2 cable will run from micrologix PLC to Net AIC and panel view will communicate through DH485 port of NET AIC. While connecting HMO2 cable will run from NET AIC to ENI module to connect PLC with ENI module.

Did you want an ethernet network or a dh485 network? I think (but somebody correct me if I am wrong), the PLC will work on both networks depending on its revision/model, but you will be limited to DH485 comms if that is the type of panelview that you have.
 
Why don't you go for a MiroLogix 1500 LRP series which has two Communication port - One port you connect to existing Panelview on DH485 and other Port you connect to NET-ENI ..
 

Similar Topics

I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
156
Am asking if we can upgrade sd ram and cf card of panel view plus ab by a normal sd ram and cf card but Allen Bradley to save cost because in ab...
Replies
9
Views
275
I can't seem to get the Panel View Plus 7 standard edition to downgrade to V_11, when I check the AB downloads and compatibility websites for this...
Replies
1
Views
122
Good morning, I have a question, I would like to know if I can send an Excel file to an email from my panel view and see how it is possible to...
Replies
1
Views
145
I want to run a factory talk view ME project in a Panel View Plus 7 Performance HMI. The project was developed in a 'Windows 7 Professional 64 bit...
Replies
5
Views
328
Back
Top Bottom